no earth on lighting r1+r2 what do you put on sheet | Page 3 | on ElectriciansForums
Discuss no earth on lighting r1+r2 what do you put on sheet in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
thanks. I got their in the end
Personally I'd put a c2 code on the EICR as I'd class no cpc as a potentially dangerous situation although there's no immediate risk they certainly could be. let's face it who's going to argue with you. If it's not safe it's not safe
I'd put the c2 code on your Observations sheet and put Lim in all the boxes regarding test results sheet. Also if you want put an operatonal limitation on your Observations sheet explaing why no tests have been carried out on the circuits in question.
in my book no cpc on any pvc pendant or switch whether pvc or not is a c2 many times I have gone to many
jobs and found metal switches on pvc surface boxes . pvc surface boxes they come with lugs for the cpc yes
How is it a Limitation when the conductor is not present to do the reading in the first place. It is Not Applicable. Is it not like putting the absence of rcd testing as a Limitation because none Exist?
westward 10 the man. you said about that daves code recommendation on ecir point me in the write direction please
Most people on here share the opinion that if there are no accessories which require an earth then Code 3, if there are unearthed Class 1 accessories then Code 2 as fault protection is not provided. This must be your decision though, some people feel Code 2 regardless of the current situation due to the fact that in the future an unknowing person may fit a Class1 fitting or accessory to the system no matter how many notices you stick on the CU.
I like this answer, as on the day of the test it is what you find. Just like the MOT test.
Reguarding the future modifications is that not down to the suitably qualified Electrician carrying out the work refusing to modify the circuit if it does not comply to the current version of BS7671.
You would hope so but while people can go to B&Q and buy all sorts of bits the risk will always be there.
Unfortunately you are correct. However we can only look after ourselves, and when one of us visits each n 5 years time it may be a code 2 and we can charge to correct. HOPEFULLY.
it ok for the government bring in a law. form that fat j Prescott and the grabbing bodies are not advertising on tv about part p or in the papers neither.
so jo blogs will go down to b&q and get the gear . savy
I see your point regarding the limitations, in regards to what code it should be dose it not matter about your un erthed back box & lid screws that someone could come in to contact with regardless of if your light switches are class 2.
Reply to no earth on lighting r1+r2 what do you put on sheet in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
In my opinion that is incorrect as the cpc could be broken but parallel paths may not suggest this. From previous threads you clearly have issues...