To be honest I would never take a generic error code as equating to a specific problem being present. An error just means the instrument you're using can't give a meaningful reading so you need to investigate further with another instrument or tester that can.
 
but i put an earth rod in but still no earth

That statement doesn't make sense, if you put a rod in then there will be an earth but it might be high impedence (high IR). You really need some proper test results. Maybe try to beg or borrow an alternative tester.

Your test result of 0V L-E also doesn't make sense, if you added a rod then any digital tester would show a voltage L-E even if the Ra is extremely high.
 
Have you tried it with another tester, even a voltage/continuity tester.

i know you've proved it in other locations but this install should be on, so i'd double triple check.
 
Matey, go back in the morning and redo some of the tests and then things may become clearer.

Please let us know what you find...but you should have seen this when you did a Ze prior to taking the old board off.
 
polarity in fine. Did not test before changing the ccu as it was for an mate for his rental property so just got in and done it and now problems. A big mistake i made.
 

Reply to No earth reading! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
268
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
755

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
1K
  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top