third party story so dont shoot the mesenger just wanted to share this and see if any of are fellow sparks have come across this my mate goes to a house to investigate why there is no earth into property this has come to light as the gas board wont install new boiler as there is no earth how right they were aswell. the supply is a tnc-s the incoming cable has been put into a hennely block (jb) as the meter has been re moved to outside by scottish power so the meter reader can read without access into property. so meter now outside with a new 2 core 16mm ran to outside length roughly 10metres (not right) scottish power come out today and say there is no brass plate in hennly block (jb) which provides the earth. in effect this property has been in a potenially dangerous condition. scottish power are to put this right sorry for long winded story your thoughts please
 
Ok mech I get what your saying so how could an electrician provided an earthing arrangement in this case because to do so you need to get the dno involved anyway to reconnect the pme head is out of bounds the dno guy came out and reinstalled the pme head live something us electricians are not allowed to do would you agree and if so then how the hell were we ment to do it with out the dno

Again........ if they provide an earth terminal then they have a duty to maintain it.
 
With new connections and we are talking new, cant speak for other suppliers, we fit self connect meters or isolation switch, no ZE taken, NO earth conductor fitted, all new cut outs have red/black plug on cover of ne link, for access to the electrical contractor to make his connections.
 
With new connections and we are talking new, cant speak for other suppliers, we fit self connect meters or isolation switch, no ZE taken, NO earth conductor fitted, all new cut outs have red/black plug on cover of ne link, for access to the electrical contractor to make his connections.

Some of your people do take a Ze! They wrote it on the head when ours was done a few weeks ago.
 
Yes, it was a service move rather than new service but they completely removed the old on and installed a complete new service from a different pole rather than joint and extend etc.

They fitted a new head and isolator with the old meter and wrote the measured Ze on the head. They didn't connect the tails or earth though.
 
Yes, it was a service move rather than new service but they completely removed the old on and installed a complete new service from a different pole rather than joint and extend etc.

They fitted a new head and isolator with the old meter and wrote the measured Ze on the head. They didn't connect the tails or earth though.

WPD, are the DNO on my patch. Mpan 11
 
That's a bit different then, I forget not everyone has the DNO and meter operator as the same company.

In this area new services and service alterations they always fit or move the meter.
I've had issues when straying in to what was EDF territory where they wouldn't move the meter on an alteration.
 

Reply to no earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
1K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top