G

gimpchop

Hi i had my garage converted in to a office about 5 years ago. Today i went out to my garage and there is no electric. I have checked the mcbs in the garage and they are all in the correc possitions and allso the main mcbs in the house and all are in the correct positions can any one point me in the right direction in to trouble shooting it pls.
 
Hi rhanks for the reply. Yes there is a fused spure from my main fusebox in the house but it hasnt tripped the mcb in there either.
Might seem a daft question, but that z-spa on for all those hours would be quite a heavy load, you haven't burnt out a main L or N in the Garage CU have you, due to a loose connection?
 
Hi done a little testing. With a voltage tester there dont seem to be any power from the mcb on the main fuse board. Ive teaced the cable from fhe fuse board to a join where it comes from the house to the armored cable and there is no power there either.
 
Hi done a little testing. With a voltage tester there dont seem to be any power from the mcb on the main fuse board. Ive teaced the cable from fhe fuse board to a join where it comes from the house to the armored cable and there is no power there either.
Join what sort of joint? a wacky one?
 
Last edited:
If you know how long it will take to fix and what it will cost then presumably you already know exactly what has happened, so why don't you tell us what the fault is?
I might be wrong but I think LankyWill is assuming it will be a simple fault to find, not that he knows what the fault actually is.
 
Hi i have traced the problem it seems the main rcd in the garege cu melted due to the lay-z-spa. Can i ask a few questions regaurding it.
1. Why did it melt and not trip out as it should?.

2. Is 100a enough to run the spa as i intend to run it from there in the future.?

3. How can i prevent it hapening again?.

4. Can i legally change it myself or do i have to have a electrician to do it?.
We are a little worried as it could have caused a fire.
Thanks for any info.
 
Ps There is a join where it comes out the house and to armored cable it is a conector block in a waterproof box.
I am a cctv installer but not by any means a electrician but i know basics.
 
If you know how long it will take to fix and what it will cost then presumably you already know exactly what has happened, so why don't you tell us what the fault is?

Its only a simple fault Dave hardly string theory, any spark worth his salt could find it with an MFT in a short amount of time. Bearing in mind the OP wont know the simple fault finding process that we do. Fallout with your missus?
 
Its only a simple fault Dave hardly string theory, any spark worth his salt could find it with an MFT in a short amount of time. Bearing in mind the OP wont know the simple fault finding process that we do. Fallout with your missus?

What is the fault? The only information we have is that there is no power in the garage but no protective devices appear to be tripped.
It could be a simple five minute fix or a couple of hours finding the hidden joint which has failed.
 
Hi i have traced the problem it seems the main rcd in the garege cu melted due to the lay-z-spa. Can i ask a few questions regaurding it.
1. Why did it melt and not trip out as it should?.

2. Is 100a enough to run the spa as i intend to run it from there in the future.?

3. How can i prevent it hapening again?.

4. Can i legally change it myself or do i have to have a electrician to do it?.
We are a little worried as it could have caused a fire.
Thanks for any info.

1. An RCD does not operate on overload, it only operates on current imbalance, this is why you must also have overload protection in the form of an MCB or fuse.

2. 100A is the normal maximum rating of a domestic supply, if your spa needs that much current then you will need a commercial electricity supply to run it.

3. Get an electrician to investigate why this has happened and work out what needs to Ben done to fix it and prevent it happening again.

4. There is no law preventing you from changing it, but unless you know why it has failed and fixed the cause of the failure then just replacing the RCD will result in the same thing happening again, potentially with worse consequences such as a fire.
 
Hi i have traced the problem it seems the main rcd in the garege cu melted due to the lay-z-spa. Can i ask a few questions regaurding it.
1. Why did it melt and not trip out as it should?.

2. Is 100a enough to run the spa as i intend to run it from there in the future.?

3. How can i prevent it hapening again?.

4. Can i legally change it myself or do i have to have a electrician to do it?.
We are a little worried as it could have caused a fire.
Thanks for any info.

If the main RCD in the garage CU has "melted" then you should isolate the supply to the garage CU immediately and call an electrician.
 

Reply to No electric in my garage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
548
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
199

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top