Just put a new cu in started testing .so here it goes start doing rfc line 0.33 nn 0.32 cpc 0.55
Ins all good now this a split load
Dis the cpc what i was working on and now showing earths in and are out so theor is no parallall paths has far that i can see the main earth is out but showing earths all water and gas have been disconnected
 
Any metal stud work in the property? a lot of other trades use the metal stuff rather than timber these days. often find boxes joined to the metal studwork.
Also any chance of damp or moisture in the walls between back boxes if they have the cpc in them?
Came across something similar when I was still at college and just started working. property had a bad damp problem that once sorted out resolved the irregular readings??
 
This is where Wander Lead is so so useful :)

IMG_1051.JPG


Gratuitous reposting of Wanda Ventham
 

Reply to Now i am pulling my hair out in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
750
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

  • Question
That 'stranded 2.5mm' was probably imperial 7/.029 which is about 2.9mm2. Which might account for expected readings being different.
Replies
6
Views
420
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
484

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top