Now i am pulling my hair out | Page 3 | on ElectriciansForums
Discuss Now i am pulling my hair out in the UK Electrical Forum area at ElectriciansForums.net
buzzlightyear
Nearly Esteemed
star command
Just put a new cu in started testing .so here it goes start doing rfc line 0.33 nn 0.32 cpc 0.55
Ins all good now this a split load
Dis the cpc what i was working on and now showing earths in and are out so theor is no parallall paths has far that i can see the main earth is out but showing earths all water and gas have been disconnected
They havent had RSJ's put in if knocking through walls or extensions etc? wouldnt be first property where somebody decides to bond the RSJ or a cable gets caught on it during its run.
An isolated RSJ should not affect the reading.
Check voltage from line ,to earth you socket tester may be giving you a false indication of a earth , by the way is it a good idea to remove the cpc then make the circuit live ? , and what is the issue here , you have a parallel earth path? Ps now i know my spelling is bad but maybe you should take off your space gloves so you may have a better chance of hitting the correct letters ☺
the only circuit which was live was up stairs ring no earths connected but showing earths ,considering it a empty house .
All cpc's and earthing has been disconnected from the Consumer Unit, and you have now energised the circuits?
Why have you energised a circuit with no cpc's connected?
how discovered
the earth was not in play when doing a r1+r2 to see if I had the wright circuit by leaving off the earths when putting the socket and see tester in to indicate that a had that circuit .and then it showed me earths present when the cpc earths not connected .
Reply to Now i am pulling my hair out in the UK Electrical Forum area at ElectriciansForums.net
That 'stranded 2.5mm' was probably imperial 7/.029 which is about 2.9mm2. Which might account for expected readings being different.
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...