Now i am pulling my hair out | Page 4 | on ElectriciansForums
Discuss Now i am pulling my hair out in the UK Electrical Forum area at ElectriciansForums.net
buzzlightyear
Nearly Esteemed
star command
Just put a new cu in started testing .so here it goes start doing rfc line 0.33 nn 0.32 cpc 0.55
Ins all good now this a split load
Dis the cpc what i was working on and now showing earths in and are out so theor is no parallall paths has far that i can see the main earth is out but showing earths all water and gas have been disconnected
I'm with Sparkdog here
I wouldn't rely on a plug tester for anything.
Perhaps there is supplementary bonding somewhere, it used to be taken off the nearest cpc.
My guess supp bonding under the bathroom floor between earthed copper pipe and your RFC earth.
I still don't see what you are hoping to find or achieve here. It could be supplementary bonding, it could be metal dual boxes. It's a parallel path somewhere. If I was the customer I wouldn't like to be paying for all this unneeded work.
sorry if I repeat anything said/done.....but forget the plug in tester. Use your multimeter on all RFC's dead test end to end & also test for any cross over of RFC's r2 on cct1 to r2 cct2 (neutrals as well)etc and RFC r2 to the met with other ccts attached...anything ?
If you want to work live test at sockets removing neutral from cct ?
If I understand correctly, you have one specific RFC that has a connection to earth somewhere, despite the installation earth & bonding connections all being disconnected?
As others have mentioned, I'm not totally understanding why this is a problem? I'm assuming nothing is tripping, and you just want to know why, rather than needing to disconnect this other earth? Normally I'd just move on.
Assuming you really do need or want to know, then can you not just split the RFC into two, and find which half is still earthed. Then repeat with the earthed bit, until you narrow it down? Just like looking for any other fault on an RFC?
And when you say earthed, are you measuring a resistance to the suppliers' earth? If so, what value (from each end of the RFC)? Or did I recall seeing you are measuring Zs values on this RFC (with main earth and bonding disconnected)?
Usually it's me trying to find out why something does not compute - go Buzz go !
Perhaps confirm IR on that circuit and then isolate any backbox connections. With 23.6 Ohms it sounds like there's "an earthrod" attached :) .
Reply to Now i am pulling my hair out in the UK Electrical Forum area at ElectriciansForums.net
That 'stranded 2.5mm' was probably imperial 7/.029 which is about 2.9mm2. Which might account for expected readings being different.
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...