After a sleepless night of ----ing and turning worrying that i had been coding my EICR's wrong i decided to take the matter to a higher level than us mere mortals, the NICEIC tech support.
This is the outcome.
C3 should be given for socket outlet circuits that do not have RCD protection which are not liable to be used for portable equipment ie: 1st floor
C3 should be given to circuits that have cables buried in the wall less than 50mm without mechanical protection.
C3 should be given to circuits that supply bathrooms etc and supplementary bonding as correct.
C2 should be given to socket outlet circuits that do not have RCD protection which are liable to be used for portable equipment ie: ground floor
C2 should be given to circuits supplying bathrooms etc if the supplementary bonding is incorrect.
I do believe that i understand the concept Mr G Sparks
I do believe that i am not scaring any body by suggesting RCD protection in some form Mr Dillb
I do not think by correctly coding the RCD protection issue on a EICR is giving the trade a bad name, only those who incorrectly carry out their job do that Mr Murdock
its time for me to celebrate this slam dunk
arty: