T

Tomac1980

Hi, please can someone advise. I have completed the domestic installers course which was great but it did not cover outside lighting. I would like to install an outside light in my garden and due to the position I would have to bury the cable underground. There are no blanks in the DB and would really like some advice
Thanks in advance
 
The thing that scares me most is that there's thousands just like him out there, at least he had the sense to ask a question even if the answer he got wasn't what he wanted. Many others swallow the line that they're now competent.
 
If it's going outside into the garden, which is a special location under the regs and Part P, and being run from an existing circuit it will require a minor works certificate and notification to building control - because it's in a special location. Whoever notifies the work should be Part P registered.
To fulfill the requirements the light must be 30mA RCD protected and earthing and bonding should be to the current requirement of BS7671:2008(2011). SWA burried in the ground should be to a depth of 600mm where anyone may be likely to dig, with a warning lable approx 150mm above it. Ideally the cable should be laid on a bed of sand and also covered over with sand before backfilling. If the cable is going under hard standing ground (patios, paving slabs, concrete, tarmac etc) it is reasonable to reduce this measurement to 300mm. If you are connecting to an existing socket circuit that is not RCD protected I would use an RCD spur switch with a 3 amp fuse and run the cable through the wall into a Wiska box. (Make sure the cable is protected by if it crosses the cavity.) Terminate the twin and earth with the SWA there and don't forget the earth link and the banjo. It's easier than taking the SWA into the house. Also drill the drain hole in the box where it is marked otherwise damp may collect there.
If your circuit you are connecting to is already RCD protected then do exactly the same, just use a normal DP spur switch with a 3 amp fuse.

Good luck
 
This thread may seem harsh to the outside world.

But some people just need to be told straight whether the OP likes it or not, he's not an electrician no matter how much he thinks he is.
i`m gettin fed up with know-knowts mark that just carry rite on.....
but to attempt install....without knowin about earthin n bondin.....lolffs
 
If it's going outside into the garden, which is a special location under the regs and Part P, and being run from an existing circuit it will require a minor works certificate and notification to building control - because it's in a special location. Whoever notifies the work should be Part P registered.
To fulfill the requirements the light must be 30mA RCD protected and earthing and bonding should be to the current requirement of BS7671:2008(2011). SWA burried in the ground should be to a depth of 600mm where anyone may be likely to dig, with a warning lable approx 150mm above it. Ideally the cable should be laid on a bed of sand and also covered over with sand before backfilling. If the cable is going under hard standing ground (patios, paving slabs, concrete, tarmac etc) it is reasonable to reduce this measurement to 300mm. If you are connecting to an existing socket circuit that is not RCD protected I would use an RCD spur switch with a 3 amp fuse and run the cable through the wall into a Wiska box. (Make sure the cable is protected by if it crosses the cavity.) Terminate the twin and earth with the SWA there and don't forget the earth link and the banjo. It's easier than taking the SWA into the house. Also drill the drain hole in the box where it is marked otherwise damp may collect there.
If your circuit you are connecting to is already RCD protected then do exactly the same, just use a normal DP spur switch with a 3 amp fuse.

Good luck
he wont know how to ring n gland a bit of armoured....
bet they dont show that on these `courses`.......
 

Reply to Outside light in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Is it a retaining wall? If so I'm of the opinion penetrating damp is almost impossible to avoid. Make a channel underneath for runoff and slosh...
Replies
5
Views
577
It's unlikely tht a small domestic garden pump and a single lamp will come anywhere near close to overloading even the smallest (3A) fused spur...
Replies
2
Views
401

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top