Hi i have a double oven which is 5.8kw and induction hob which is 7.4kw there currently isnt a cooker circuit in the house but there is 2 spaces in the CU so am I correct in thinking I can put 2x32A breakers in and run 6mm cable to both .
Jack a 7.4 KW hob will draw max 32.2 Amps and a 5.8 KW oven will draw Max 25.2 Amps you will need to apply Diversity to those calcs, best advicget an Electrician to design and install circuits to suite the needs.
A lot of (sparks) hmm, would struggle with that question, let me remind everyone the new appliances will also come with instructions, now even though as an electrician you should be able to work out the load and cable size, the instructions will also have their own minimum cable size suggested as well lol, that will confuse a lot here, not all of us have enough experience to know what cable is needed automatically or whether one supply is enough for both units.
His profile says Quals Part P & 17th so not to be rude to the OP this should be well within what he has been taught. I am hoping that the OP knows the answer but is doubting himself.
That will be all down to Part P then Ant cus the 17th teaches you jack all, except how to pass an exam. Neither qualification will class you as an Electrician. Well maybe it does these days. Part P is a building regulation NOT a qualification.
Reply to Oven and cooker circuits in the UK Electrical Forum area at ElectriciansForums.net
I believe the 6mm and 40A MCB debate is a little contentious at times. It depends on the installation method, being pretty close to the tabulated...
I actually did it with a 4 core 4.0mm swa last week!