Hi i have a double oven which is 5.8kw and induction hob which is 7.4kw there currently isnt a cooker circuit in the house but there is 2 spaces in the CU so am I correct in thinking I can put 2x32A breakers in and run 6mm cable to both .
Discuss Oven and cooker circuits in the UK Electrical Forum area at ElectriciansForums.net
do the eggs come with strips has well.this is an earth hen.
Deleted
A barkers dozen?do the eggs come with strips has well.
if they do ,order a barkers dozen.
that's better ,post 27.A barkers dozen?
Keep up PeteA barkers dozen?
he got to oil his zimmer frame first. .Keep up Pete
Buzz bluddy altered that you cheaterKeep up Pete
You aintfar off the button there Telhe got to oil his zimmer frame first. .
it's only by continuing working that i keep the legs from seizing up. the brain seized years ago.You aintfar off the button there Tel
I think a bit of 6mm will murder it, as usual.I prefer to apply diversity to each separate appliances (in excess of 10A) individually, as opposed combining their total loads, then using formulae.
What do ya think?
I think a bit of 6mm will murder it, as usual.
Why would you do that thenI prefer to apply diversity to each separate appliances (in excess of 10A) individually, as opposed combining their total loads, then using formulae.
What do ya think?
Hi new on here and back on the tools after years of point at stuff for others (so go easy). I understand diversity, but with an induction hob it is quite easy to put all rings on and be drawing max load (think Sunday dinner of all the family). The same with the oven when heating up. For the sake of another cable (there is a spare way) and future proofing, why would you not run 2 x 6mm cable on 2 x 32A breakers?
try bosh induction hob ,not 1.5mm cable but 4mm.Depends on how they are made. I have installed induction hobs that are rated at a total load of over 6kW yet are supplied with 1.5mm flex and a 13A plug top.
I prefer to apply diversity to each separate appliances (in excess of 10A) individually, as opposed combining their total loads, then using formulae.
What do ya think?
Why would you do that then
Yes, my mate wired in 6.0mm for hob and when he got it only had 13A plug top couldn't believe it.Depends on how they are made. I have installed induction hobs that are rated at a total load of over 6kW yet are supplied with 1.5mm flex and a 13A plug top.
Ah your mateYes, my mate wired in 6.0mm for hob and when he got it only had 13A plug top couldn't believe it.
Yes, my mate who I work with who is the other 50% of Charltec Electrical Ltd not to be confused with (new) members imaginary mate that is going to wire that house etc.Ah your mate
Reply to Oven and cooker circuits in the UK Electrical Forum area at ElectriciansForums.net