Hi i have a double oven which is 5.8kw and induction hob which is 7.4kw there currently isnt a cooker circuit in the house but there is 2 spaces in the CU so am I correct in thinking I can put 2x32A breakers in and run 6mm cable to both .
 
I prefer to apply diversity to each separate appliances (in excess of 10A) individually, as opposed combining their total loads, then using formulae.

What do ya think?

Why would you do that then

My understanding of diversity, is that any one electrical cooking appliance, through thermostats etc and switching, would never be able to use its full load, e.g. a simple single electric oven, has a selector switch, to select either main oven or grill, not both together.

Using Table A2 in the OSG for household installations; it shows formulae for diversity & asking for f.l. of connected cooking appliances.

Manufacturers would supply the f.l. figure for their devices. Separate appliances may function differently (as described above).

Further into Table A2, calculating diversity for commercial premises, it makes allowances for more than one appliance, not withstanding the different scenario.

In a simple set up of separate hob & oven, the usage is not comparable, however as is the fashion these days to have more than one oven, combination ovens etc etc, it is not hard to see the usage these appliances could have. Therefore, in such an install, I would calculate diversity separately.

In most cases as Sparksburntout suggested, 6mm would muller most situations.
 
MDJ, every time a keep looking at your avatar .Im thinking I sure that f**King dog is going to kill some one .one day!
The dog is calm, the forum needs to watch out if I re-introduce shrek.
 
Bit late but to be fair to the OP he doesnt say he is an Electrician in his profile.
yeah but... mdj does not say he's a dog in his profile, but his avatar says he is.
 

Reply to Oven and cooker circuits in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
358
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
326
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
369

Similar threads

I believe the 6mm and 40A MCB debate is a little contentious at times. It depends on the installation method, being pretty close to the tabulated...
Replies
3
Views
311
  • Question
I actually did it with a 4 core 4.0mm swa last week!
Replies
12
Views
762

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top