twin / parallel feeds are pretty common on submains larger than 300mm.

struggling to think of anything else to add to be honest lol.

er , carry on.

;-)
 
hoo hoo Can I join in this thread?? I'll invite Eng54 as well... :)
 
Parallel circuit/supply needs all conductors to be of the same CSA, follow the same route, cables be of the same type and construction. Parallel circuits can consist of several conductors/cables not just two. Such circuits can and do offer many advantages over a single much larger conductor/cable installation....

If designing the OP's circuit from scratch probably 2 X 16mm would be selected, but in some circumstances even 2 x 10mm could replace a single 35mm cable....
 
so, in a nutcase, sorry, nutshell, as OP already has a single 25mm, the solution is to parallel a second 25mm cable in.
 
i already said it in post #6.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Parallel Supplies
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
58

Advert

Thread statistics

Created
Guest 004,
Last reply from
Chr!s,
Replies
58
Views
8,608

Advert

TrueNAS JBOD Storage Server

Back
Top