Sorry was back at work.

I initially thought about 10m. But probably about 14 to 15m
 
Dansk was right, the technical man needs to get more technical, you need a minimum of 4mm but most would use 6mm cable for this length.
Looks like you may have more disruption, get them to change it.
 
Thanks Earthstore & Dansk.

He said all their systems they have used 2.5mm and some they have had SMA out to replace inverters and they hadn't made any comments about the cable.
 
If I can get technical, then why cant the technical man


Allowable Voltage Drop1 %
Run Length14 m
Current Demand16 A
System Voltage240 V
Voltage Drop10.71 mV/A.m
Recommended Cable Size6 mm[SUP]2[/SUP]
 
As always you guys are spot on. A quick look through the manual shows up a Min AC cable size of 6mm up to 23m distance

Mounting instructions state "Do not mount the Sunny Boy on flammable construction materials". Does this mean a fire retardant board? Is it like plywood with plasterboard or something?

Also my RCCB is 30ma

[ElectriciansForums.net] Peak output


[ElectriciansForums.net] Peak output
 

Attachments

  • [ElectriciansForums.net] Peak output
    SMAMountingInstructions.jpg
    60.5 KB · Views: 78
Last edited by a moderator:
You're already more clued up than their 'technical' expert.

They may have used 2.5mm on all of their other jobs - this doesn't make it right. It just means that they have done all of their other jobs incorrectly also.
 
Masterboard - we use it all the time - Masterboard

Any GOOD builders merchant will stock it or similar, it's not cheap, (ÂŁ120 / sheet) though one sheet of 8 x 4 will do 4 jobs easily. (4 x 2 per inverter..)

It's stronger than pasterboard, tends to be water resistant also, doesn't have the paper finish.
 

Reply to Peak output in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

  • Question
Part III:). I think I have clarity-having spoken to my electrician who installed my heaters, he said that the part of my fuseboard that is...
2 3 4
Replies
52
Views
2K
Thank you so much for your input! I will speak to octopus and see what they say regarding a new tariff.
Replies
13
Views
523

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top