Dansk was right, the technical man needs to get more technical, you need a minimum of 4mm but most would use 6mm cable for this length.
Looks like you may have more disruption, get them to change it.
 
Thanks Earthstore & Dansk.

He said all their systems they have used 2.5mm and some they have had SMA out to replace inverters and they hadn't made any comments about the cable.
 
Just followed along the cable run and I would say 13m from isolator to Gen meter.

Is there an online calculator for this?
 
If I can get technical, then why cant the technical man


[TABLE="class: data, width: 795"]
[TR]
[TD="bgcolor: #DCDCDC"]Allowable Voltage Drop[/TD]
[TD="bgcolor: #DCDCDC"]1 %[/TD]
[/TR]
[TR]
[TD="bgcolor: #DCDCDC"]Run Length[/TD]
[TD="bgcolor: #DCDCDC"]14 m[/TD]
[/TR]
[TR]
[TD="bgcolor: #DCDCDC"]Current Demand[/TD]
[TD="bgcolor: #DCDCDC"]16 A[/TD]
[/TR]
[TR]
[TD="bgcolor: #DCDCDC"]System Voltage[/TD]
[TD="bgcolor: #DCDCDC"]240 V[/TD]
[/TR]
[TR]
[TD="bgcolor: #DCDCDC"]Voltage Drop[/TD]
[TD="bgcolor: #DCDCDC"]10.71 mV/A.m[/TD]
[/TR]
[TR]
[TD="bgcolor: #DCDCDC"]Recommended Cable Size[/TD]
[TD="bgcolor: #DCDCDC"]6 mm[SUP]2[/SUP][/TD]
[/TR]
[/TABLE]
 
As always you guys are spot on. A quick look through the manual shows up a Min AC cable size of 6mm up to 23m distance

Mounting instructions state "Do not mount the Sunny Boy on flammable construction materials". Does this mean a fire retardant board? Is it like plywood with plasterboard or something?

Also my RCCB is 30ma

SMAGridConnection.jpg


SMAMountingInstructions.jpg
 

Attachments

  • SMAMountingInstructions.jpg
    SMAMountingInstructions.jpg
    60.5 KB · Views: 85
Last edited by a moderator:
You're already more clued up than their 'technical' expert.

They may have used 2.5mm on all of their other jobs - this doesn't make it right. It just means that they have done all of their other jobs incorrectly also.
 
Masterboard - we use it all the time - Masterboard

Any GOOD builders merchant will stock it or similar, it's not cheap, (£120 / sheet) though one sheet of 8 x 4 will do 4 jobs easily. (4 x 2 per inverter..)

It's stronger than pasterboard, tends to be water resistant also, doesn't have the paper finish.
 

Reply to the thread, titled "Peak output" which is posted in the under the Solar PV Forum | Solar Panels Forum on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top