There is no requirement for Consumer Units to be protected by an RCD, so no code at all.
You should note and code each instance where RCD protection is required, but is not present
For instance:
for circuits of a location containing a bath or shower,
for socket-outlets intended for general use by ordinary persons,
for socket-outlets used for mobile equipment outdoors,
and for cables concealed in walls at a depth less than 50mm.
Most would warrent a code 4 or 2, depending upon how dangerous you consider the lack of RCD protection to be, and to which edition the installation, and any additions or alterations were conducted to.
 
hi guys was wondering what code you would give a consumer unit with no rcd protection??? code 1 0r 4???
demetri

Hi Demetri,

Have you carried out many periodic inspections?

Your questions worry me slightly, talking of 'consumer units without RCD protection' , '60898 fuses' and then deliberating between a code 1 and a code 4 to allocate to a defect?

Maybe your questions are academic and you're doing the 2391-10?
 
One small point to add, its not satisfactory to have one or two RCD's to BS 61008 protecting more than one circuit. each circuit, as described in previous post by spinlondon, should be protected by an RCBO to BS 61009
 
Last edited by a moderator:
One small point to add, its not satisfactory to have one or two RCD's to BS 61008 protecting more than one circuit. each circuit, as described in previous post by spinlondon, should be protected by an RCBO to BS 61009


So what BS number are the RCD's in a dual RCD consumer unit think you'll find they are BSEN61008 , an RCBO is a combination of MCB and RCD where the 61008 is just an RCD so as long as the out going circuits are protected by an MCB then you can have as many circuits as required , if you install an RCBO in a consumer unit with a 61008 both at 30ma then you will end up with no discrimination for the RCD/RCBO's
 
Last edited by a moderator:
The failure of one circuit, say a cooker with an earth fault, will trip the RCD, causing the loss of any other circuit also protected by that RCD This is in conflict with 314.1 and 314.2. i hope that will explain "Why not?"
 
Noo you are mis under standing that reg when you design an installation you design it to reduce any incovieniance if an RCD trips for instance you would install the upstairs lighting on the same RCD protected circuits and the down staires sockets ,for circuits that are likly to trip an RCD ie garage shed hot tub you would install on independant circuits protected by RCBO's or and MCB depending on what the circuits is suppling , thats why we have 17 edition consumer units some hi integrety where you can use RCBO,s and RCD protected MCB's idealy you would install all circuits on RCBO's i grant you that but you can protect more than 1 circuit with a 61008
 
Last edited by a moderator:
Nickblake there is no such thing as a 17th edition consumer unit, its how you configure the board that will determine whether or not your installation complies. i will agree with you that not every circuit needs RCD protection.

If you look at the list supplied earlier you will see where RCBO's are indicated. any other circuit must be individually assessed. the garage shed that you mentioned, being outside the equipotential zone is a case in point and needs RCD protection

For cascaded RCD's the upstream RCD could be a time delayed or Type S with an ordinary RCD after that. in the case of your shed the TDR could supply the cable to the shed (to protect the cable) and an RCBO to protect the tub circuit etc. this will provide discrimination between the two RCD devices and give the best protection.
 

Reply to PIR codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
424
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Commonly known as double knock, some pirs have a latch on time delay for a few seconds, giving time for the 2nd one to activate .
Replies
3
Views
366
You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top