Hi confused-fuse,
second bit...
Code 3 (Requires further investigation) – Indicates that usually the inspector was unable to come to a conclusion about this aspect of the installation or the observation was outside the agreed purpose.
Examples:-
1 Unable to trace final circuits
2 Unable to access equipment or connections needing to be inspected that are known to exist but have been boxed in such as by panels or boards that cannot be easily removed without causing damage to decorations.
3 Insulation resistance of less than 1 mega ohms between live conductors connected together and earth, when measured at the consumer unit with all final circuits connected. If any one circuit has an insulation resistance of less than 20 kilo ohms, a code 2 recommendation should be given.
4. Absence of a main equipotential bonding connection to a lighting protection system conductor, where it is not known by the inspector if it is required to protect against lightening side flashes. (Absence of other main equipotential bonding connections would usually warrant a code 2).
Code 4 (Does not comply with BS 7671 as amended)
Examples:-
1. Switch lines not identified as line conductors at terminations (for example, a conductor having blue insulation is not sleeved brown in switches or lighting points).
2. Circuit protective conductors or final circuit conductors in a consumer unit not arranged or marked so that they can be identified for inspection, testing or alteration of the installation.
3. Undersized main bonding conductors (subject to a minimum size of 6mm²), if there is no evidence of thermal damage.
4 Absence of circuit protective conductors in circuits having only Class II (or all insulated) luminaires and switches.
5 Protective conductor of a lighting circuit not (or incorrectly) terminated at the final circuit connection point to a class II (or insulated) item of equipment, such as at a switch mounting box or luminaire.
6 Absence of ‘Safety Electrical Connection – Do Not Remove’ notice.
7 Absence of a notice indicating that the installation has a wiring colours to two versions of BS 7671.
8 Absence of RCD periodic test notice
9 Absence of circuit identification details
10 Sheath of an insulated and sheathed non-armoured cable not taken inside the enclosure of an accessory, such as at a socket-outlet or lighting switch.
11. Bare protective conductor of an insulated and sheathed cable not sleeved with insulation, colour coded to indicate its function.
12 Installation not divided into an accurate number of circuits to minimise inconvenience for safe operation, fault clearance, inspection, testing and maintenance.
13 Fixed equipment does not have a means of switching off for mechanical maintenance, where such maintenance involves a risk of burns or injury from mechanical movement
14 Absence of supplementary bonding to installed Class II equipment where required (such as in a bathroom or shower room, in case the equipment is replaced with Class I equipment in the future).
15 Reliance on a voltage-operated earth-leakage circuit-breaker for fault protection (protection against indirect contact – fault protection).
16 Absence of RCD protection for cables installed at a depth of less than 50 mm from a surface of a wall or partition where the cables do not incorporate an earthed metallic covering, are not enclosed in earthed metalwork, or are not mechanically protected against penetration by nails and the like.
17 Absence of RCD protection for cables concealed, at whatever depth, in a wall or partition the internal construction of which includes metallic parts (other than metallic fixings such as nails, screws and the like) where the cables do not incorporate an earthed metallic covering are not enclosed in earthed metalwork, or are not mechanically protected to avoid damage to them during construction of the wall or during their installation.
18 Absence of RCD protection for socket-outlet circuits that are unlikely to supply portable equipment for use outdoors, or that are in a bathroom.
19 Absence of supplementary bonding where required, such as in a bathroom or shower room, where all the following three conditions are not satisfied:
a all final circuits of the location comply with the requirements for automatic disconnection, and
b all final circuits of the location have additional protection by means of a 30 mA RCD, and
c all extraneous-conductive-parts of the location are effectively connected to the protective equipotential bonding (main earthing terminal).
Source: NICEIC Domestic Periodic Inspection, Testing and Rep