everything is possible , unless its not lol , I'm going to check when back on site next week to begin 2nd fix , but fairly happy with the 84mm route , however interested in the loop test result at the db so going to make it the 1st install
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss PME head , builder forgot earth cable , 100amp 3phase supply , 10 bedroom house , 10 bedroom house in the The Welcome Forum area at ElectriciansForums.net
Without a paddle, and an earthwireShort of running a separate cpc you are well and truly up the creek.
Well if it's in the regs, then it's in black and white....just seems maddnes having a good earth at the DNO cutout, then at the DB end ditching it and then put in earth rod. Again , the University has several of its own substations with massive section boards that feed other large buildings (so technically the substation is the DNO supply) so then there'll be say 3 or 4 300mm2 SWA cables go out to feed other buildings, no separate cpc, then when they enter the building, an earth conductor is took off the armour to an earth bar and then from that you'll have a main protective conductor to the buildings section board, and protective earthing conductors to other services.
Yeah it's mostly TN-S around the UniThat doesn’t sound like a PME supply, so the requirements for bonding conductors in that situation are likely to be different.
See the original post "as I directed" if the OP has instructed the builder what to install, I can't in all honesty see how it would be the buider's fault, the OP told the builder what to do, so down to the OP imo.Looking at the size of the job, get it dug up and done properly.
Builder's fault...he carries the can.
''the builders installed a 35mm 4core swa as i directed however they forgot about a 16mm earth''.See the original post "as I directed" if the OP has instructed the builder what to install, I can't in all honesty see how it would be the buider's fault, the OP told the builder what to do, so down to the OP imo.
True, good point, did matey mention the 16mm2 earth? only he can tell so come on OP spill the beans, did you or didn't you instruct the builder to install the earth wire?''the builders installed a 35mm 4core swa as i directed however they forgot about a 16mm earth''.
Are we getting the full facts, Pete?
Agree, but what were your instructions exactly? did you tell them to run the SWA and an earth cable?yep, however they supplied the cable , my input was instruction only, so as long as it is correct to the regs I'm now happy
Their cock up thenyes 35mm swa 4core and 16mm earth was the instruction
yes 35mm swa 4core and 16mm earth was the instruction