We recently had a thread, perhaps someone else can find it (I don't have time now to trawl) about connecting a load over 13A to an RFC. Careful study of the regs seemed to indicate that a B16 MCB is permissible in place of a 13A fuse to BS1362. That would allow the existing oven to be connected to a 32A circuit.
If that is the case, notwithstanding the recommendation for all large loads to be supplied independently of a general socket-outlet RFC, I do not think there is much to gain by changing the oven to one with a lower maximum current. The power used during cooking under thermostatic control depends on the heat loss from the oven, not the rating of the elements. There are some subtleties here that I won't go into now but suffice to say the effect of a slightly lower element rating on the usability of the circuit for other loads isn't worth the cost and effort of changing the oven.