S

SammyG

Greetings all,

I'm looking for a bit of advice. I'm not actually an electrician, but I am an electrical design engineer and I am aware of the regs.

I recently bought a new house which, after a few weeks developed an earth fault in the kitchen that kept tripping the RCD. No problem - I found the issue and fixed it.

However, whilst I was investigating this, I noticed that the sockets in my kitchen are not on a ring circuit, but rather in a radial circuit, with 2.5mm cabling, but the MCB in the consumer unit was a 32A. I believe that this was unsafe, so I replaced the MCB with a 20A.

Because I am a designer rather than an installer, I don't know how common this is and I don't really know how dangerous it is - theoretically, in fault conditions, the wire would likely melt before the MCB trips, but does it work this way in practice?

Also, I suspect that I am not technically supposed to tinker with my own electrics this way, so I am reluctant to go down any official channels.

I'd like to know if you folks here agree that this was dangerous, and if so, should I report the original installer to anyone (his name and number are printed on the consumer unit)?

Thanks in advance

Sammy.
 
Do you have a copy of the regs? If so appendix 15 gives recommendation for RFC & Radial, and suggests a 20amp ocpd for 2.5 tw&e on a Radial circuit . Table 4D5 gives current carrying capacities for insulated & sheathed flat cables, the highest rating for 2.5mm tw&e is 27amp clipped direct.
 
From your description, it was non-compliant with BS7671 using the 32A MCB as the cable was not protected against overload, however I would not consider it to have been especially dangerous. Unless the cable installation method had drastically reduced its Iz, it certainly would not have melted and probably not got very much above rated temp even with the breaker at full load, which in itself would have been rare. Nonetheless, as it was a new installation, it should have been compliant and you could reasonably expect the installer to rectify at his cost. If the 20A radial arrangement does not provide an adequate supply given the expected use of the socket-outlets served, then rectification might include completing the ring or adding a circuit.

Edit, just realised it was a NEW house.
 
Last edited:
Think the horse has bolted now, might have been better to get rectified by the company responsible for the new build, but I suppose at least its as it should, albeit you haven't the required competency (you said a much yourself) to do so. Are there any other 'noughties' in the installation? And are your neighbours in the same boat?
 
Get a spark in sammy, i understand your a designer but from an installer point of view, you dont know the ins and outs of the install side. Top marks on finding the fault but keep yourself safe and get a pro in.
 

Reply to Potentially dangerous - should I report this to someone? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
Well yes obviously, but if the transformer is indoors and your lights are 50m down the garden then it's very easy to need pretty big cables at...
    • Like
2 3
Replies
42
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top