Well not quite ...

You'd need one both ends, and the grid supply end would need to be time delayed, as you want the the Inverter end one to trip first and then the grid end one.

If you only have one at the inverter end, the cable would still be 'live' to the grid'
If the grid end one isn't time delayed, then you can't guarantee to trip the inverter one first, and if you don't it would still be powered by the inverter.

Hence why we design out the requirement :)

Why is that?
 
Why would the PV supply be connected to the load side of an RCD?
PV is a secondary supply and should be connected at or very near to the origin of the installation.

There is one hell of a difference between where it should be connects and where some idiots actually connect it.

The trouble is that the inverter is mounted remotely from the CU, so there is a cable run from the inverter to the CU. if that cable gets chased in then it would need RCD protection.
 
Ok, having slept on this and thought a bit more about the regulation 551.7.2 (iv) I think this may not be quite as clear cut as I first thought.

The regulation actually allows the PV to be connects on the load side of the RCD provided that the RCD disconnects all live conductors and that the inverter supply is not reference to earth. The theory being that the RCD disconnecting both L and N from the grid will disconnect the earth reference from the inverter supply and therefore make the inverter output floating with respect to earth and so not deliver a shock (in the same way as electrical separation).
This however raises the question of whether the inverter output is fully isolate from the earth? And of course what happens in the case of a N-E fault on the load side of the RCD?
 
Well not quite ...

You'd need one both ends, and the grid supply end would need to be time delayed, as you want the the Inverter end one to trip first and then the grid end one.

If you only have one at the inverter end, the cable would still be 'live' to the grid'
If the grid end one isn't time delayed, then you can't guarantee to trip the inverter one first, and if you don't it would still be powered by the inverter.

Hence why we design out the requirement :)

Which of course wouldn't comply as you can't have a time delay on a 30mA RCD used in this way.

It could be done using a shunt trip on a DP breaker at the PV end triggered by an aux contact on the supply end RCD.
 
Why isn't time delayed acceptable? That's what was suggested by our NICEIC assessor in a similar situation


Or is it the 30mA time delay that you are saying isn't acceptable? - I didn't quote values...
 
Last edited:
Why isn't time delayed acceptable? That's what was suggested by our NICEIC assessor in a similar situation


Or is it the 30mA time delay that you are saying isn't acceptable? - I didn't quote values...

A time delayed RCD won't disconnect in the required time.

If the RCD is 100mA for fault protection in a TT then it would have to be time delayed at both ends for the usual reasons. A non-TD RCD at the PV end wouldn't discriminate with the 30mA RCDs used elsewhere in the installation.

If they are 30mA RCDs providing additional protection in the usual manner then they have to disconnect in 300mS at 30mA
 
Hi

Interesting thread, PV is not an area im involved in but i would like to know more.

It seems to me that the PV supply needs to be connected upstream of all final circuits, connection made via a CPD.

With regards to a RCD on the PV ac supply, providing the inverter has simple seperation, where is the earth reference for the RCD?

Cheers
 
Hi

Interesting thread, PV is not an area im involved in but i would like to know more.

It seems to me that the PV supply needs to be connected upstream of all final circuits, connection made via a CPD.

With regards to a RCD on the PV ac supply, providing the inverter has simple seperation, where is the earth reference for the RCD?

Cheers

I know next to nothing about PV, but sources of supply are all basically the same.

That's one of the things I want to know, do all inverters have outputs which are electrically separate from Earth?
 
I know next to nothing about PV, but sources of supply are all basically the same.

That's one of the things I want to know, do all inverters have outputs which are electrically separate from Earth?

Well you can earth the d.c side of the inverter providing the inverter has seperation.

Now the seperation is there to stop d.c current feeding onto the a.c side. Now where simple seperation is not provided by the inverter then a type b rcd needs to be installed.

Cheers
 
LV 3 phase inverters.
In particular the ABB Trio range.
Although there are separate connections for each phase, neutral and earth, the earth and neutral are connected together internally.
In fact it appears that the neutral is nothing more than another earth conductor, as there is no internal connection from the neutral to any other part of the inverter.
 
Last edited by a moderator:

Reply to Pv on rcd in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
894

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top