Well not quite ...
You'd need one both ends, and the grid supply end would need to be time delayed, as you want the the Inverter end one to trip first and then the grid end one.
If you only have one at the inverter end, the cable would still be 'live' to the grid'
If the grid end one isn't time delayed, then you can't guarantee to trip the inverter one first, and if you don't it would still be powered by the inverter.
Hence why we design out the requirement
Why is that?