S

srl-8

Hi All,

In preparation for a pending assessment, I have installed a new 2 way CU in my garage with all new wiring (my own property), and TT the earth. (House supply is TNC-S, PME).

I am testing the lighting circuit. (6a mcb / 2 switches / 2 way/ 1.5/1.0 cable . Have tested in all switch positions. Polarity is correct.

I am getting Ra/ZE value of 145 ohms.
I am getting measured ZS of 147 ohms at the last light

These results suggested I should get a R1 +R2 of 2 ohms.

I am getting a result of 2.7 ohms.


Being new to testing, does this R1 + R2 result seem acceptable to you ?

I would value the comments from people on here.

Regards
 
Hi All,

In preparation for a pending assessment, I have installed a new 2 way CU in my garage with all new wiring (my own property), and TT the earth. (House supply is TNC-S, PME).

I am testing the lighting circuit. (6a mcb / 2 switches / 2 way/ 1.5/1.0 cable . Have tested in all switch positions. Polarity is correct.

I am getting Ra/ZE value of 145 ohms.
I am getting measured ZS of 147 ohms at the last light

These results suggested I should get a R1 +R2 of 2 ohms.

I am getting a result of 2.7 ohms.


Being new to testing, does this R1 + R2 result seem acceptable to you ?

I would value the comments from people on here.

Regards

You have calculated R1 & R2 by Zs-Zdb (Ze would be at PME cutout). What was your dead test R1 + R2 for lighting circuit? Also do you have an RCD Main Switch in Garage DB as they can add quite a bit to your reading? Did you test both Zdb and Zs on three lead (No Trip) test?
 
Zs-(R1+R2) will always be higher than a Zdb,Ra or Ze due to parralel paths. Think you need to use the tables in GN3 and work what your R1+R2 should be and see if they are satisfactory.
 
i can't see why you can accept that TT Ra value when you have a perfectly good TNC-S earthing system. is there any valid reason why you've not used it?
 
Measured R1 +R2 was 2.7 (highest reading I got, from all switch positions.
ZE at garage board (earth electrode/TT) 143 ohms
Measured ZS = 147 ohms

Yes RCD, 30ma main switch.

Does this result look correct ?
 
I am getting Ra/ZE value of 145 ohms.
I am getting measured ZS of 147 ohms at the last light
These results suggested I should get a R1 +R2 of 2 ohms.
I am getting a result of 2.7 ohms.
Being new to testing, does this R1 + R2 result seem acceptable to you ?

If I understand correctly, you first measured R1+R2 (before any live tests) and got a value of 2.7 Ohm?
If so, and then subsequently measured Zs on this circuit as 147 Ohm, with a Ze of 145 Ohm, I'd say at these values, the accuracy is limited by the accuracy of the tester (you are not going to measure exactly 147.7 Ohm, the MFT is just not that accurate).
 
the results looks about right, but see my last post. a 145 ohm Zdb is not, in my eyes, acceptable. what have you used for a rod, a coat hanger?
 
Measured R1 +R2 was 2.7 (highest reading I got, from all switch positions.
ZE at garage board (earth electrode/TT) 143 ohms
Measured ZS = 147 ohms

Yes RCD, 30ma main switch.

Does this result look correct ?

No, for a single garage lighting circuit 2.7 Ohms R1 + R2 is way to high. <0.50 Ohms would be more like it. Something is amiss there.
 
Last edited:
teltrix,

There is no parallel path to my knowledge. The garage is supplied via a 2 core swa. Because the House is TNC-S, I was advised not to export the earth in case of a netrual/earth fault.

So have TT the garage. Does that make sense.

(UPDATE: The garage was originally earthed to a dis-used copper pipe, disappearing in the floor. )
 
Last edited by a moderator:
teltrix,

There is no parallel path to my knowledge. The garage is supplied via a 2 core swa. Because the House is TNC-S, I was advised not to export the earth in case of a netrual/earth fault.

So have TT the garage. Does that make sense.

(UPDATE: The garage was originally earthed to a dis-used copper pipe, disappearing in the floor. )
Not really, no
 

Reply to R1+R2 - two way lighting - 2.7 ohms, can i get your opinions please? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
886
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks again for your help, now solved 👍
Replies
11
Views
692
"It works" and "it's safe" are not necessarily the same thing. With DIY work, they are often far from the same thing.
Replies
7
Views
725

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top