Which scheme will be assessing you? It is not unknown for a scheme to insist the value has to be under 100 Ohm - and the scheme in question believes it has more authority than BS7671!
 
No offence, but you are going to have to really brush up for your assessment, they wont hold your hand, they will expect you to know. Understand what Ze, Zdb & Zs mean. Also when you test,you need to have expected values, otherwise you are just guessing. Like Dillb said read GN3, and then read it again, it is all in there mate.

GN3. Riveting.
 
TJ Anderson - This was what I thought, but somehow my 145 ohms reading on a TT (under 200 is considered stable) has got everyone suggesting not to use a rod..?

That is their preference and obviously lower is better. IET On site guide says over 200 is considered unstable so it there in black and white.
 
Which scheme will be assessing you? It is not unknown for a scheme to insist the value has to be under 100 Ohm - and the scheme in question believes it has more authority than BS7671!

Not NICEIC, Stroma. I will check to see if they are happy with the 144 reading
 
and a RCD that hasn't been tested for donkeys? i'd rather rely on a tried and trusted method of disconnection. too much faith is placed in these made to a price, not quality, get out of jail free, if you can't provide a decent earth. either use the pme or install some decent rods.
 
Is your tester calibrated, and working correctly? Is it worth testing the installation with a different meter just for peace of mind?

I, d be inclined to check the connections regarding that high R1 + R2 reading. Most likely something as simple as a poor termination.

Regarding the earth rod, although acceptable I wouldn't be happy with that reading. Surely using the swa armour is a better option if it is indeed an option?
 
Not NICEIC, Stroma. I will check to see if they are happy with the 144 reading

hum, Stroma assessments, to my knowledge are far more extensive than the others so I hope you brush up a lot before you sign the cheque.

And why did you do live tests knowing that the dead tests were very high?
 

Reply to R1+R2 - two way lighting - 2.7 ohms, can i get your opinions please? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
226
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
973
Thanks again for your help, now solved đź‘Ť
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top