no. you should have extended the equipotential zone, using the armour as cpc/earth. the only problem you'd have is if the garage has extraneous parts, you may need to run a separate 10mm bonding conductor.
 
Leesparkykent - sorry, thanks for clearing that up. Wrong term being used. The only means of earthing for the garage is a earth rod.
 
Trev - No I don't expect that to make a massive difference, but that's why im on the forum... to ask for advice. I think this r1+r2 value is high... what would you expect to get on a 2 way lighting circuit?
 
Trev, Are you say do away with the earth rod and use the swa for the earth? I will need to check if the armor is connected at the house end...

Although, you are not happy with 145 ohms, below 200 is considered stable as you know..?
 
Trev, Are you say do away with the earth rod and use the swa for the earth? I will need to check if the armor is connected at the house end...

Although, you are not happy with 145 ohms, below 200 is considered stable as you know..?

it bloody well better be. and with a proper gland. otherwise, i don't give you much hope for your assessment.
 
Trev, Are you say do away with the earth rod and use the swa for the earth? I will need to check if the armor is connected at the house end...

Although, you are not happy with 145 ohms, below 200 is considered stable as you know..?
That's pretty much exactly what I'm saying mate, if the armour isn't connected then it's not that big a deal to put that right.
 

Reply to R1+R2 - two way lighting - 2.7 ohms, can i get your opinions please? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
527
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
931
Thanks again for your help, now solved 👍
Replies
11
Views
950

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top