no. you should have extended the equipotential zone, using the armour as cpc/earth. the only problem you'd have is if the garage has extraneous parts, you may need to run a separate 10mm bonding conductor.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss R1+R2 - two way lighting - 2.7 ohms, can i get your opinions please? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
How long is the 3c?
Leesparkkent - export earth (meaning, use the swa as a means of earthing. ) I have not used this and TT garage instead.
export the earth?
Trev, Are you say do away with the earth rod and use the swa for the earth? I will need to check if the armor is connected at the house end...
Although, you are not happy with 145 ohms, below 200 is considered stable as you know..?
That's pretty much exactly what I'm saying mate, if the armour isn't connected then it's not that big a deal to put that right.Trev, Are you say do away with the earth rod and use the swa for the earth? I will need to check if the armor is connected at the house end...
Although, you are not happy with 145 ohms, below 200 is considered stable as you know..?