Having re-read your original post, if I understand correctly, the 2.7 Ohm R1+R2 is just for 1 light in the garage, with 2 way switching (switches at front and back of garage, I assume). I which case, it appears somewhat high. You know what cable size you have used, and can estimate the length to the nearest metre, including the additional 2-way switching length - you can use table F6 in the On Site Guide to estimate the R1+R2 (last column of table, Volts Drop, is in fact resistance in milliOhm/metre).

If this is for an assessment, I'd be surprised if the assessor did not query a Ze of 145 Ohm, I wouldn't be happy with a value that high. You could put in a decent earth rod (not a 1 metre long 3/8 twig, but something more substantial and longer). Or you could take note of some of the other posts suggesting you do this differently.
 
TJ, Even though this is a 2 way switch, so will measure the 3 core cable aswell.... ?
Test all to verify and record highest value which should be at the furthest point of the circuit. Regarding TT or extending PME, either is compliant, is it up to you. Do you have anything extraneous in your garage that would require bonding?
 
That's pretty much exactly what I'm saying mate, if the armour isn't connected then it's not that big a deal to put that right.

What does not comply with what he has done? Nothing wrong with TT. if he wants to. The only issue it seems is a high R1 +R2 on garage lighting circuit.
 
For someone who is about tomstart doing work on peoples homes this is quite scary that the OP doesnt even know what to do or work out what is wrong here, even with all the advice given.

Still I suppose the scams wont mind ££££££££££££££££££
 
SDJ - You have understood correctly, I will test the ze at the garage board using the swa as the earth tomorrow and see what result I get. I presume I will be looking for a sub- 0.35 ohms being a tnc-s system.

As for the high r1+r2.. ill have to go through It again tomorrow.
 
SDJ - You have understood correctly, I will test the ze at the garage board using the swa as the earth tomorrow and see what result I get. I presume I will be looking for a sub- 0.35 ohms being a tnc-s system.

As for the high r1+r2.. ill have to go through It again tomorrow.

please go and have a read of GN3 that will explain testing and the procedures.

Youmdo know there is only one place to take a Ze reading dont you?
 
SDJ - You have understood correctly, I will test the ze at the garage board using the swa as the earth tomorrow and see what result I get. I presume I will be looking for a sub- 0.35 ohms being a tnc-s system.

As for the high r1+r2.. ill have to go through It again tomorrow.

The swa should be earthed at the supply side even if you are not using it as the earth for the garage db. Why would the Zdb need to be below 0.35? It is not the Ze of the installation.
 
TJ Anderson - This was what I thought, but somehow my 145 ohms reading on a TT (under 200 is considered stable) has got everyone suggesting not to use a rod..?
 
SDJ - You have understood correctly, I will test the ze at the garage board using the swa as the earth tomorrow and see what result I get. I presume I will be looking for a sub- 0.35 ohms being a tnc-s system.

As for the high r1+r2.. ill have to go through It again tomorrow.
No offence, but you are going to have to really brush up for your assessment, they wont hold your hand, they will expect you to know. Understand what Ze, Zdb & Zs mean. Also when you test,you need to have expected values, otherwise you are just guessing. Like Dillb said read GN3, and then read it again, it is all in there mate.
 
The swa should be earthed at the supply side even if you are not using it as the earth for the garage db. Why would the Zdb need to be below 0.35? It is not the Ze of the installation.

Simonslimline - Sorry, this is my first garage (outbuilding), so ZE is at origin at main House supply. What is the equivalent at the garage end..
 

Reply to R1+R2 - two way lighting - 2.7 ohms, can i get your opinions please? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
527
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
931
Thanks again for your help, now solved 👍
Replies
11
Views
950

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top