R1+R2 - two way lighting - 2.7 ohms, can i get your opinions please? | Page 5 | on ElectriciansForums
Discuss R1+R2 - two way lighting - 2.7 ohms, can i get your opinions please? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
What does not comply with what he has done? Nothing wrong with TT. if he wants to. The only issue it seems is a high R1 +R2 on garage lighting circuit.
There is nothing wrong with making a decent TT mate, I do it often. What's worrying me is that the OP seems to have been talked into doing something which he seems unsure of by someone who hasn't got a clue.
What is wrong with extending a perfectly sevicable TN-C-S when it is available.
This cut-off copper pipe which was previously being used as the earth for the garage, what Ra did it give you? I assume you did actually test it before you decided it was not ok to keep as an earth.
The earth electrodes you have installed, what size are they? How long are they? How many positions and how far apart are they?
Why are you unsure as to whether the SWA has been earthed at the supply end? This must be done regardless of what you have done at the load end.
Are there any extraneous parts in the garage which need main bonding? (I suspect the previously mentioned copper pipe is, unless you have go grid of it completely)
The CSA of the armouring, I've got a table somewhere showing the CSA of each size SWA, I think a 2 core SWA has armouring equating to 16mm2
16mm2 of what, Steel?? You require the equivalent of 10mm2 of copper to comply with bonding requirements for a typical domestic PME supply, and 16mm of steel doesn't come close. Copper has 8 X the conductance of steel!!
I think the OP is going to have a hard time explaining this buckshee garage installation to any assessor!! Not that it'll matter too much, as i have no doubt he'll still get his badge of competence!!
Did he not qualify the statement by asking if there were any extraneous-conductive parts?
Now now, I'm sure the OP is highly competent and you're just being mean. We've no time for those sort of comments on here as they imply that he in fact isn't, and what's more, comments that question the competence of other people automatically become impolite no matter how they are asked! So you go away you nasty man. Hang your head in shame!
I'm sure the totally unbiased assessor will find no fault whatsoever with this installation. In fact, I would go as far to say that the OP's willingness to shun that terribly unreliable PME connection with a horribly low Ze value in favour of what is inevitably a highly stable and widely accepted as best practice TT connection with a brilliantly high Ze value, utilising nothing but the best 3/8" rod will be applauded by him/her.
How did the assessment go srl-8? It's always nice to get some feedback..
If this was your first assessment with stroma then I'd be very impressed/suprised if they passed you first time as they are quite thorough. I'd also be interested in what they said about using a rod, rather than extending the EPZ and also what they thought of the high R1+R2, just interested.. not having a go at you..
Reply to R1+R2 - two way lighting - 2.7 ohms, can i get your opinions please? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
Thanks again for your help, now solved 👍