Hi all,
I have been to a property where the tails come out of the meter and into an RCCB which then feeds the main switch of the consumer unit. All circuits are protected by MCBs.
If I'm adding a new circuit, is it best put in an RCBO instead of an MCB?
My point was if he installs a new circuit to a board which has a RCD main switch (and doesn't need it) then in affect he will be making the existing circuits worse by adding to the problem of one RCD protecting the whole installation. I know it is not clear cut and is only my interpretation so I think a board change would ensure all the new work is compliant.
i agree, but you border on persuading the customer to spend more than necessary if a less costly solution is available whilst still leaving the installation safe. a bit like condemning 3036 boards because they're not to current standards, although safe for continued use.
Where would you use one?
I know where you find them, next to the rocking horse sh*t lol
Main and sub distribution units used for temporary power distribution in outdoor events will often incorporate adjustable RCDs which can be set to give 30mA time delayed operation along with a whole host of other possible settings.
Most rental generators now have adjustable RCD protection as standard too.
Hi Dave
But why would you want to set it at 30mA delayed as opposed to 100mA delayed , as by delaying it you will have lost the benefit of the 30mA anyway ?
Is this something to do with the regs you have to follow for events
Ok. I think we can safely say the OP's client will not have a bespoke "specialist order" variable ma RCD on the front end of his install. More like a crusty old 60A Crabtree ELCB that don't trip when the button is pressed!!
Hi Dave
To ensure discrimination with 10mA RCDs installed downstream of it. The same way you would use 100mA S type in front of 30mA in a TT setup. It depends entirely on what it is protecting and why.
You are building installations out of pre-built standard distribution boards unlike fixed installations so you almost always end up with multiple RCDs in series. Sometimes you have to set one as a 30mA time delay just to stop a fault on one circuit from tripping out 2 or 3 RCDs upstream of it but still give discrimination with a 100mA upstream of that.
There is no regulatory reason for using them though, just the individual electricians design/method for ensuring that faults cause minimum disruption.
No he won't, but you stated that such things do not exist, so those of is who know better have disagreed.
I will have a look at the RCD when I go back and update you all.
It looked like a fairly new RCD with a test button. Definately not 10+ years old! Also no adjustments available on it.
So the general verdict is;
If it's a 30mA RCD then use an MCB for new circuit.
and
If it's 100mA RCD then use a 30mA RCBO for new circuit?
it is not quite that clear cut. You will need to interpret the regs on this one as there is a little disagreement.
I would say to be 100% sure just change the board. You cannot be wrong then. Other methods are open to a little interpretation.
Prepare 2 quotes and give the customer the pros and cons of both.
Reply to RCCB as main switch? in the UK Electrical Forum area at ElectriciansForums.net
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit