Just an update on the RCD/Inverter problem. I talked to the manufacturers of the Inverters and they said that the problem is not the leakage current, as I have already tried a 100mA RCBO, but instead the Inverters are too small for the motors ( alarm bells did start ringing - bet they though a quick sale here!). The motors in question stop/start due to the work they carry out, so they said when a motor is carrying out a task that requires it to stop/start all the time, the inverter should be the next size up. Apparently this will solve the problem of tripping RCD on Inverter circuit. Looking forward to your thoughts.......
Cheers,
Just an update on the RCD/Inverter problem. I talked to the manufacturers of the Inverters and they said that the problem is not the leakage current, as I have already tried a 100mA RCBO, but instead the Inverters are too small for the motors ( alarm bells did start ringing - bet they though a quick sale here!). The motors in question stop/start due to the work they carry out, so they said when a motor is carrying out a task that requires it to stop/start all the time, the inverter should be the next size up. Apparently this will solve the problem of tripping RCD on Inverter circuit. Looking forward to your thoughts.......