[h=3]Consumer Units [/h][h=3] [/h][h=3]Definitions p25[/h][h=3] [/h][h=3]Consumerunit (may also be known as a consumer control unit or electricity controlunit). A particular type of distribution board comprising a type-testedco-ordinated assembly for the control and distribution of electrical energy,principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and anassembly of one or more fuses, circuit-breakers, residual current operated devices orsignalling and other devices proven during the type-test of the assembly assuitable for such use. [/h]
 
Statutory legislation 2394 :

There aresome areas for some of these regulations that relate specifically to Inspection.

Electricityat Work Regulations 1989
Testing & Inspectionof installations is not just to confirm compliancewith BS-7671 but to confirm compliancewith EAWR. For inspection purposes, EAWR requires that:

Onlycompetent persons should be engaged in the testing procedure (Regulation 16)
Suitableprecautions for safe isolation need to be taken (Regulation 14)
Padlocks & isolock systems should be used so that controlof isolation remains under the control of the inspector (Regulation 13).

 
2392-10 .this is what -&-s are looking for .
Although themajor-part of any Inspection will be ( Visual) Other human-senses may be employed .
 
Prior :- to RCD tests being carried-out , 2392-10. Your reason . it is essential for ( Safety-reasons) that the , Earth-loop-impedance of the installation has to been tested to check that the Earth-return-path is sound & that all the requirements have been-Met. BS-7671:

BS-7671: stipulates the order in which tests should becarried out . :icon_bs:
 
2392-10 : We do this , day-in-day-out .

Circuitry Check , What is Normal to Us . ?? The list is Endless .

All circuits shall be verified through switching-operationto ensure that the circuits are installed in accordance with the designated-circuit

On / Off switching ofthe lighting circuit to ensure that the lighting circuit is installedcorresponding to the lighting-switch, protective-device and labelling

Switchingof the power-circuit to ensure that thecircuit corresponds to the ( Protective-device(s) such as RCD, RCBO & MCB,and that the protective device performs in accordance with the designated duty

Switching of the main-switch/ isolator to ensure the corresponding-circuit is propererly-controlled by themain , switch / isolator , 100A

Ensuringall the ( Protective-devices ) perform properly against the designatedcircuit

if Normal, then switch onall other out-going switches , one-by-one . ( does this justify , fault-finding ) Lighting .

What have you , “ Verified “ Circuitry-Check :13:
 
BS-7671:2008:2011: States P/24 :icon_bs:

Circuit. An assembly of electrical equipment suppliedfrom the same origin and protected against overcurrent by the same protective device(s).

" Periodic-Inspection, EICR " whichreports on the condition of the Existing-installation.
 
State therecommended sequence of tests and the reasons for that sequence :svengo:

State therequirements which need to be considered for protective conductors in the termsof
( ProtectiveConductors )
Circuit-protective-conductors

Conductor-continuity: 2392-10 .

All Ring-final-circuit-conductor(s) including theprotective conductors have been tested for Continuity.

Conductor(s) Continuity-test-results ( You have achieved your Verification )

Polarity check results recorded

P/393 . MEIWC: Verification – Polarity-satisfactory .
P/397 . EICR : Verification– Polarity-satisfactory . (Confirmation of supply-polarity)
p/402 . GSoTR : Verification– Polarity-satisfactory . ( Correct supply-polarity-confirmed )

Consumer-units : P/400 . Re-cap 2392-10.

4.7. Operation of main-switch ( Functional-check) 612.13.2.
4.8 . Manual-operation of circuit-breakers & RCDs toprove disconnection . 612.13.2.
4.9 . Correct-identification of circuit-details & protective-devices . 514.8.1. 514.9.1. Etc .

 
Cables connected up with Correct-polarity. ( 2392-10 your main Achievement) Polarity / Continuity-method

All Ring-final-circuit-conductor(s) including theprotective conductors have been tested for Continuity.

Conductor(s) Continuity-test-results ( You have achieved your Verification )

 
Wording , Exams

Recognise a Schedule of Inspections as being an Essential part ofthe documentation required for either an , Initial-verification or Periodic-inspection
( Schedule of Inspections – for New –installation-work-Only ) P/395

P/399 . Condition-report-inspection-schedule . Guidance for the Inspector
Note: BS-7671:2011: Has stated the facts . :icon_bs:

(1) Section 1.0 , Where ( Inadequacies ) in the DNO-equipment are encountered the inspector should advise the personordering the work ( To inform the Appropriate-Authority )

 
2392-10
Understand the , onerous-responsibility associated with the completion ofelectrical-installation-certificate. EIC
This Safety-Certificate has been issued to confirm . Etc

 
Inspection Schedule . P/395 :iagree:

The Inspection-Schedule provides confirmation thata ( Visual-inspection ) has been carried out asrequired by Part 6 of BS-7671 and listsall the inspection requirements of Regulation - 611.3.


 
Scheduleof Test Results . 2392-10 . :icon_bs:

The Schedule of Test-Results is a ( Written-record) of the results obtained when carrying out the electrical-test(s) required by Part 6 of BS- 7671. The following notes give guidance onthe compilation of the schedule, which should be attached to the ElectricalInstallation Certificate.

 
Minor Electrical Installation Works Certificate

Scope
onlyto be used for additions to an electrical-installation that do not include theintroduction of a , New-circuit ( BS-7671 Regulation 633.1). :icon_bs:


 

Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

thanks for the confirmation this is what i thought. i cant think of what use this device is . i have seen David Saverys Arc Fault Detection Device...
Replies
4
Views
449
  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top