2394: Your making an Assessment of ( PFC ) Protective-fault-current . ( PSCC ) & ( PEFC ) 612.11.
Useful-junk .
What is ( PSCC ) &why is Loop-résistance important .
By using . Ohms-law . the Loop-résistance will - determine the maximum-current that can flow around a circuit .
Example - Loop-resistance !! . 1Ω . & the supply-voltage . 230V
Voltage / résistance = current . ( 230V ÷ 1Ω = 230Amp ) themaximum-current that could flow would 230A .
If we think about . fault-conditions . ?? . soif we had an Appliance that was “ Dead-short-circuit “ as wecan see a circuit-breaker (Protective-device - 32A )
Protective-device ( 32A ) . is lower than ( 230A )
Rule of thumb . Appendix - 4 . BS-7671:2011:
Circuit has a measured ( Zs ) of 0.51Ω - (Your Measured Value is 0.51Ω )
Protected by . Type C - 32A . BS-EN-60898 . MCB
Table 41.3. Maximum permissible ( Zs ) C - 32A . 0.72Ω
Multiply the maximum permissible value by .( 0.8 ) : 0.72 x0.8 = 0.57Ω . This now becomes the . maximum permissible value .
The measured-value is less than this . ( 0.57Ω less than 0.72Ω ) the circuitPassed .
2394 : this isall you have to know . at this Mo .
( Circuit-loop-impedance ) Thisis a Live-Test .
Method of earth-fault-loop-impedance - ( Zs ) testing at . socket-outlet . ( Circuit ) total-earth-fault-loop-impedance can be Measured by ( plugging a ) . earth-fault-loop-impedance-tester. into Socket-outlet
-&-s . BS-EN-61557-3 . - Earth-fault-loop-impedance-tester .
With the same Tester . GN-3 . p.83
These-instruments may also offer additional-facilitiesfor deriving . Prospective-fault-current . ( PFC )
2394 : Question . Why “ Dead-Tests “
Firstly : performed on an Installation - prior to Energisation .
“ Dead-Tests “ will . if carried-out correctly .Indentify-faults . within any Circuit .
610.1. Every-installation shall . during erection & on-completion ( before being putinto service ) be Inspected &Tested . to verify . so far is reasonably-practicable . that the requirementsof the regulations have been met .
2394: Studying is the part of understanding .
O.S.G.- p.18 . Domestic whereUnskilled-persons have access for there Use . Class - 11 . Enclosure .
Asthe regulations rightly put it . Under the control of Ordinary-persons .
Consumer’sControlgear .
Consumer-Unit. to BS-EN-60439-3 . Annex ZA . is foruse on single-phase-installations up to 100A . may include thefollowing-components . 530.3.4.
- Double-pole-insulator.
-Circuit-breakers . or RCBOs for protection against . Overload &Fault-currents .
-RCDs for additional-protection against Electric-shock .
-RCDs for . Fault-protection .
Containing. Protective-devices .
AnnexZA . ( Informative) 530.3.4.
Split-load “ Example .
100A- Double-pole ◄► ( A ) circuit . & Two-RCBOs - circuit 1 . 2 . 3 - spare / way
RCD- 30mA ◄► ( B ) circuit . 6 -Way . - circuit . 4 . 5 . 6 . 7. 8 . 9 - spare / way
RCD- 30mA ◄► ( C ) circuit . 6 -Way . - circuit 10 . 11 . 12 . 13 . 14 . 15 - spare / way
Formy old notes . Useful-junk .
Circuit-breaker.
Instantaneous-trippingwill occur within . 0.1s . within the range of currents which are multiples ofthe nominal-rating of the device ( In )
16A- type B . will disconnect a fault in . 0.1s . when the . Fault-current is in the range of . ( 3 x 16 = 48A . 5 x 16A = 80A ) .
Instantaneous-tripping- ( In - 3x )
In ) rated-current or current-setting of . protective-device .
Circuit-breaker. a device-designed to open & closea circuit by . No-automatic-means .&to open automatically on a predetermined-overcurrent .
RCDtest-instrument needs to supply a range of Test-currents appropriate to thedevice being tested & display the time-takenfor the device to operate .
p.84. GN-3 . reminds us . To check RCD operation & to minimise danger during the test . thetest-current should be applied for no longer than . ( 2s)
Not in . GN-3 or Regulations .
Oneof the principal-requirements is that under any-circumstances the duration of the . Test-current . cannot exceed ( 2s ) this makes it possible to test most ( Time-delay-devices ) which have been installed to . ensure-discrimination. between RCDs of different-operating-currents
The. Test-current . for a full ( 2s ) without the RCD operating .
Ifthe device should trip it is possible that there could be . nuisance-tripping
Third-testto be carried out to the RCD x5-time . rated at no more than 30mA for these devices we must carry out a test at. five-time ( x5) the rated current .so our 30mA device this will be at 150mA . when this test is appliedthe device should operate within a time of . 40mS . that is - 0.04s . ( 5 x 30 = 150mA )
30mA/ 100mA . Discrimination
Discriminationbetween RCDs is archived by using a . time-delay . This allows . sufficient-time for the RCD .protecting the final-circuit todisconnect the circuit . before the main-RCD operates . speed of operation has to be . 0.04s - with five-times therated-tripping-current . ( 5 x 30 = 150mA )
UsefulJunk .
2394: Lets go back to Basics . for the sakeBS-7671:2011: RCD - mA . What’sin a amperes ( A )
30mA- IΔn ) is the rated-residual-operating-current ofthe RCD . so if we take it in Amps - 0.03A
Milli : divideby 1000 . 30mA = RCD - 30 ÷ 1000 = 0.03A . amperes
100mA ÷ 1000 = 0.1A
300mA ÷ 1000 = 0.3A
500mA ÷ 1000 = 0.5A
Characteristicsof protective-device - BS-EN-60898 & BS-EN-61009-1 . Overcurrent-protective-devices to comply with .
Three-tripping-characteristic B . C . D .
Tripping-characteristic → ( Btype ) Etc .
32A . BS-EN-60898 - B type .
Measured-value is 0.93Ω . Atthis stage you have only measured . ( itis Not the Maximum- Zs )
2394 . As the regulation tells us . Zs at 70°C - Maximum . forthe circuit . PVC - T&E . 32A / 1.44Ω .
Current-carrying-capacity . Table-4D5 .
Themaximum-current which can be carried by a conductor under-specified-conditions. without its steady-state-temperature . exceeding a specified-value .
Firstly: 70°C - thermoplastic-insulated & Sheathed-flat-cables . T&E . with -protective-conductor - Copper-conductor(s)
Ambient-temperature- 30°C
Conductor-operating-temperature - 70°C
So no calculations are needed . in this case .
Loop-impedance. Of the cable limits the electricity during a fault .
Maximum ( PSCC ) at thesupply-terminals has been quoted by . DNO as 16kA .
External( Ze ) can be calculated by . Uo /If . 230V ÷ 16000 - ( If ) = 0.014375 Ω . rounded up . 0.0144Ω
Providedby the DNO. Maximum-fault-levelat ( Point ) itis Known .
BS-EN-60898 . in our case . Circuit-breaker . 6kA . 230 ÷ 6000 = If . ???
Point to note . p.55. Circuit-breakers.
Thevalues specified in .Table - 41.3. for the types & ratings ofovercurrent-devices listed may be used instead of calculation . ◄◄
Circuit-breakerare sized to protect the integrity of the cable-insulation .
BS-EN-60898.
Circuit-breakers- for Overcurrent-protection for household & similar-installations
differencebetween the Two-short-circuit-ratings. ( Icn ) & ( Ics - Short-circuit-current at theOrigin ) of the circuit .
GN-3. p.56 . “ the two must not be confused “
(Icn ) is the maximum-fault-current thedevice can . interrupt-safely . although it may no longer be usable .
(Ics - A ) is the . maximum- fault-current the devicecan interrupt-safely without-loss of performance .
Two-short-circuit-capacity-ratings- are defined in . BS-EN-60898 & BS-EN-61009-1 .
Current-carrying-capacity . Table-4D5 .
Themaximum-current which can be carried by a conductor under-specified-conditions. without its steady-state-temperature . exceeding a specified-value .
Ido feel these a need to harp on about . Circuit-breakers . so am on rant - mode .
32A- Circuit-breaker BS-EN-60898 - B . valueof ( Zs - 0.98Ω - your measured-value ) . 5 x32A = 160A . 230V ÷ 160 = 1.4375Ω .
5x 32A - ( If ) fault-current = 160A . fig.3.4. reminds us that . Prospective-current - rms . Amperes
2394: Table - 41.3. . Example . in our case here . ( Zs -circuit-loop-impedance ) 32A / Zs . 1.44Ω :
Zs ≤ 230V ÷ 160A = 1.4375Ω . lets round it up . 1.44Ω . making me . Maximum- earth-fault-loop-impedance . ( Ief )
Line-conductor - Protective-earth ( PE ) T&E
Fault-loop- determination of measurement . ( Circuit-loop ) Ring-final-circuit . Radial-circuit .or final-circuit.
Impedance- Verification . Fault-loop-impedance . in or case . ( Zs ) Earth-fault-loop-impedance . ( 2394 : Circuit-loop-impedance Ω )
-&-s- question(s) . whether you canunderstand & calculate the . ?? following-procedure .
calculatethe . Design-current . for each-circuit . PS in this case a Cooker .
Ib = P/V
Ib = 14000 / 230V .
-&-s- ( Ib ) = 10A + 30% ofthe remainder . + 5A for the socket .
Ib= 29.5A
Pointto note : O.S.G. - p.176
Cooker-circuitsin household & similar-premises .
Therating of the circuit is determined by the . assessment of the current-demandof cooking-appliance(s) & cooker-control-unit-socket-outlet . if any . inaccordance with . Table-A1 of appendix - A
A - 30 or 32A circuit is usually appropriate . for household orsimilar-cookers . ( Of rating up to - 15kW )
Thankyou Dan / Jason
Thereare many Electrician’s that are Unemployed . firstly . Data-Protection-Act .
Brilliantletter to withhold or withhold consent .
Thenyou need to Protect YOUR PersonalInformation!
Job-centre-plus. What do I have to consent TO
-Privacy .
-Personal-information
-Jobseeker - agreement
-What do I have to disclosure
-a friend of mine . was asked to give out . his Email address . ( Data-Protection-Act . N/A ) his contact numbers N/A
Iwent through the Internet for him .
Pleaseread up on matters concerning the somefacts . Don’t be Bulled
[h=3]
|Consent | Welfare to Work(fare) Programmes | DWP Jobcentre ...[/h]
www.consent.me.uk/
Themost effective way of testing for . Earth-faults in wiring or equipment is by measuring the ( Insulation-résistance) 612.3.1.
The Insulation-résistance . shall be ( Measured ) between Live-conductors & betweenLive-conductors & the Protective-conductor connected to theEarthing-arrangement . Where appropriate during this ( Measurement ) Line &Neutral-conductors may be connected together .
Nails& picture hooks . screws & power-drills . a floorboard nail drivenbetween the neutral & earth fault which is likely to cause an upstream RCDto trip . The fault can be located by ( Insulation-résistance) testing . The damaged cable must be replaced & either relocated to avidfurther damage or protected . Requirements to protect cables from impact &penetration are in . regulation - 522.6.101.
(iv)B mechanically protected against damage sufficient to prevent penetration ofthe cable by nails . screws & the like .
Moisture-ingress. can cause reduced ( Insulation-resistance ) resulting in ( RCD . RCBOs . MCBs )operation . Reduced-insulation . can result from ( Wet-plaster ) condensation or water entry into accessories. Similarly some appliances may exhibit reduce-insulation causingoperation
Certain . installed servicesas heating-elements in Cookers can have reducedinsulation when Cold . the insulationincreasing when Hot .
Manufactures instructionsshould be consulted .
Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...