Direct measurement of ( Zs )
Q) . What is direct measurement ? A) . Direct-measurement ofEarth-fault-loop-impedance is achieved by use of an Earth-loop-impedance-tester.
This Instrument operates from the ( Main-supply ) making ita Live-Test .

- Instrument is fitted with a standard-13A plug.for connecting to the Installation directly through a normal-socket-outlet .
 
Thisbring home how Important it is to Test.

Zs. ( Accessory ) Socket-outlet(s) perform the test on the Outlet which is furthest fromthe Origin of the circuit .
Not-known !! . Test all . Socket-outlets inthe circuit & record thehighest-value .

 
State Three -documents on which the value of prospective fault current should be recorded .- at this point . look in page 391 . 397 .

( EIC ) - p.391 . Nature of Supply Parameters. Prospective fault current ( Ipf ) . “ 1.17 - kA “
Note - (2) . by enquiry or . by Measurement .

( EICR ) p.396 . Nature of Supply Parameters .Prospective fault current ( Ipf ) .
Note - (2) . by enquiry or . by Measurement .

GN-3 : p.57 .
Recording the Prospective fault Current . ( Ipf)
Both the ( EIC ) & the ( EICR ) contains a boxheaded . Nature of Supply Parameters , which requires the ( PFC ) at the origin to be recorded
This value to be recorded is the greater of etherthe . Short-circuit current ( Between live conductor ) or the Earth-faultcurrent ( between line conductor(s)& the main-earthing-terminal )

If it isconsidered necessary to record values at other relevant points , the can berecorded on the . Schedule of Test Results
Where . the protective-devices used at the originhave the necessary rated breaking capacity . & devices with similarbreaking capacity are used throughout the installation . it can be assumed thatthe Regulations are satisfied in this respect for all distribution boards .


 
Two-methods for measuring RCDs .

BS-EN-61557-6 . fitted with a ( standard-13A plug-top) by plugging the instrument into asuitable-socket-outlet . protected by the RCD under test.
(Appliances should be disconnected prior to Testing )

BS-EN-61557-6 . Tests are made on the ( Load-side ) of the RCDbetween the Line-conductor of the protected-circuit & the associated ( CPC) Circuit-protective-conductor

RCD-test-instrument(s)require a few . milliamperes to operate . this is obtained from the Line &Neutral of the circuit under-test .
 
Verificationof Test-results . 2394 :

Scheduleof Test-results : is a ( Written-record ) of the results obtained when carrying out theTests required by . Part-6 of BS-7671:2011:
 
Blastfrom the Past . still out there . Yeah

Measurementof ( Ze ) Three-phase .

Older-method: ( Fuses )Still out there .
Fuse(s)must be .( removed ) to disconnect theInstallation for this test .
Live-test . Red .Yellow . Blue . ( Old-colourswill be still in Use )

Three-probes
1). Probes on disconnected - Earthing-conductor
2). Probes on Neutral .
3). Probe on Line . Red . Yellow . Blue .
Red- 0.25Ω .
Yellow- 0.26Ω .
Blue- 0.25Ω .
 
Useful junk

Determine of 3phase - fault-current .

Highest . single-phase value measured . = 2.28kA .( 2.28 x √ 3 = 3.95kA )
An . approximation can be done as ( 2 x ) the reading . i.e. ( 2 x 2.28 =4.56kA )

Minimum breaking capacity for protectivedevices kA

 
( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) are the effective-résistances . to thefurthest-point
( 1.67 - relates to the ratio of résistance of . ( 2.5mm[SUP]2[/SUP] / 1.5mm[SUP]2 [/SUP] ) it won’twork for ( Other-sizes ) Ring-final-circuit Only .

( Zs ) Confirms that a (Satisfactorily-low-fault-path-exists ) to activate the . relevantprotective-devices .
 
UsefulJunk .

Nuisance-Tripping.
Certain-appliancessuch as Freezers tend to have . bynature of there construction & use . some leakage-currents to earth .

 
433.1.103. - Ring-final-circuit(s) p.81.
MinimumC.S.A. of PVC-cables . 2.5mm[SUP]2[/SUP]
MinimumC.S.A. of ( MI ) cables . 1.5mm[SUP]2[/SUP]
Minimum-current-carrying-capacityof . Line & Neutral-conductor(s) - ( Iz) 20A - device . 433.1.1
Theload-current should not-exceed what for . long-periods . Current-carrying-capacity of the cable ( Iz ) of the cable .
British-standardsof . accessories to be . BS-1363 .
Overcurrent-device to be rated at . 30A or 32A . protective-device .
 
Residual-current - Making me . ( dual-current )

TheRCD is designed to trip out when the difference between the . Line-current andthe Neutral-current ( So this is called the . residual-current) reaches the tripping-value . ( or rating ) of the device .
- Sensitivity: IΔn

RCD- Sensitivity is expressed as the rated-residual-operating-current ( IΔn ) .

TheTerm . RCD . is a generic-term applied . which open automatically in response toa . residual-current . equal to or greater than the RCDs - rated-residual-operating-current ( IΔn )
 
RCDsfall into two-categories in term of the time taken to respond . BS-EN -

(G ) General-type . These RCDs have no specified-minimum-response-time . but have specified . Maximum-response-times.
IΔn ≤ 300mS
5x IΔn ≤ 40mS .

(S ) Type : Known as . delayed-types . specified . Minimum and Maximum-response-times .
IΔn ≤ 130- 500mS
5x IΔn ≤ 150mS
 
RCDmaximum ( Zs- Ω ) or ( R[SUP]A[/SUP] - Ω )values .
IΔn- ( A ) maximum-touch-voltage - ( 50V )

30mA ) 0.03A - 1667Ω .
100mA ) . 0.1A - 500Ω .
300mA ) . 0.3A - 167Ω .
500mA ) . 0.5A - 100Ω .

- R[SUP]A [/SUP]≤ 50V ÷ 0.03A = 1667Ω . IΔn - 30mA
- R[SUP]A [/SUP]≤ 50V ÷ 0.3A = 167Ω . IΔn - 300mA
 
Test-procedure: your reason .
Theobject of continuity-testing . is to measure only the résistance of the partsof the wiring-system under test . T&E .

Whatis . Earth-fault-loop-impedance .

The path followed by . fault-current as a result of alow-impedance fault occurring between the . Line-conductor and Earth . & Earth-fault-loop . Fault-current is driven round the loop by thesupply-voltage . the amount of currentdepending on the voltage of the supply and on the impedance of the loop . The higher the impedance . the lower will be thefault-current . and the longer it will take for the circuit-protective-device operate and interrupt the fault . Loop-impedance must be low . to ensure that circuit-breakers will operatequickly enough in the event of a fault . The actual maximum-value depending on the . characteristics of the . circuit-breaker concerned . 2394: Testing of - Circuit(s) must be tested to make sure that the actual . loop-impedance does notexceed that specified for the protective-device ( Circuit-loop-impedance )
 
Whytwo -RCDs . split-load .2394 :
The circuits need to be divided evenly between two-RCDs to ensure some . lighting & power remainsif one operates .

RCD- ( G ) general-use . for Instantaneous
 

Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
917
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top