Earth-fault-loop-impedance:
Theearth-fault-loop-impedance ( Zs ) at any point in a circuit . is made up of theearth-fault-loop-impedance ( Ze ) of that part of the system external to the installation plus the sum of the impedances . in the Line and protective-conductors in the installation ( Z[SUP]1[/SUP] & Z[SUP]2[/SUP] )
Note : that for circuits rated at . Less than 100A and operating at the supply-frequency not exceeding 50Hz . it is generally considered acceptable to ignore . Inductive-reactance & to replace ( Z[SUP]1[/SUP] & Z[SUP]2[/SUP] ) by ( R[SUP]1[/SUP] & R[SUP]2[/SUP] ) the résistances of the . Line and protective-conductors .
Zs = Ze + ( R[SUP]1[/SUP] & R[SUP]2[/SUP] )
Earth-fault-loop-impedance:
Theearth-fault-loop-impedance ( Zs ) at any point in a circuit . is made up of theearth-fault-loop-impedance ( Ze ) of that part of the system external to the installation plus the sum of the impedances . in the Line and protective-conductors in the installation ( Z[SUP]1[/SUP] & Z[SUP]2[/SUP] )
Note : that for circuits rated at . Less than 100A and operating at the supply-frequency not exceeding 50Hz . it is generally considered acceptable to ignore . Inductive-reactance & to replace ( Z[SUP]1[/SUP] & Z[SUP]2[/SUP] ) by ( R[SUP]1[/SUP] & R[SUP]2[/SUP] ) the résistances of the . Line and protective-conductors .
Zs = Ze + ( R[SUP]1[/SUP] & R[SUP]2[/SUP] )