Q/As 2394 .

Which of the following is the minimum short circuit test current for a low résistance ohmmeter .

50mA
100mA
200mA
300mA

This is the requirements for the test instrument , as identified in BS-7671 Regulation 612.2.1. & GN-3 .
 
Q/As 2394 .

A continuity test is to be carried out and the instrument has been confirmed as being in calibration and undamaged , which of the following is the remaining check that needs to be carried out to confirm the instrument is suitable to use .

it is set to 230V a.c.
The battery is in a satisfactory condition
The leads comply with GS-38
it is set to read high values of résistance

The condition of the battery is the remaining check to be made on the test instrument to confirm it is suitable for use . Where the test voltage is ≤ 50V a.c. the requirement for GS-38 compliant leads is not necessary , providing the maximum short circuit is unlikely to cause a high energy flashover , The maximum current for this test is ≤ 200mA , therefore GS-38 compliant leads are nut required
 
Q/As 2394 .

Which of the following factors directly affects the conductor résistance of a cable .

a) Insulation and CSA
b) Length and CSA
c) Length and Insulation
d) Load current and CSA

of the four options given , ( b ) is the only one in which both components will directly affect the conductor résistance , Load current will only have an indirect effect on conductor résistance by raising the conductor temperature .
 
Q/As 2394 .

Two identical cables are connected in parallel , Which of the following describes the effect on the combined conductor résistance compared to the single cable .

Doubled
Quartered
Halved
No effect

The two cables will have the same résistance , which when connected in parallel will result in their combined résistance being half that of one single cable .
 
Q/As 2394 .

Which of the following factors affect the insulation résistance of a cable .

Conductor cross-sectional area
(b) Cable length
Installation method
Load current .

of the four options given ( b ) is the only one which will have an effect on the insulation résistance of the cable .
 
Q/As 2394 .

Four identical circuits are connected to a distribution board , Which of the following describes the effect on the combined insulation résistance at the ( DB ) when compared to that of a single circuit .

Doubled
Quartered
Halved
No effect

When a number of circuits are connected at a distribution board the cables are connected in parallel and so insulation résistance will be lower . in this case there are four identical cable connected in parallel and so the combined insulation résistance will be a quarter of the insulation résistance of a single cable . if the cables' insulation résistances are extremely high then this effect may not be registered by the test instrument , as the overall insulation résistance of the combined circuits may be above the upper limit of the test instrument .
 
Q/As 2394 .

A test for continuity of circuit protective conductors is carried out at every point on a circuit , Which of the following describes the purpose of this test .

To confirm correct polarity
To confirm the conductors are the correct CSA
To determine the ( R1 + R2 ) value for the circuit
(d) To confirm exposed conductive parts are connected to the MET .

of the four options given , is the only one which identifies the purpose of the test . The other three may be determined as a result of the test ,
depending on the method used , but are not the purpose of carrying out the test .
 
Q/As 2394 .

Which of the following correctly describes the relationship between prospective fault current and the fault current rating of a BS-EN-60898-1 circuit breaker .

( Ipƒ ) ≥ ( Icn )
( Ipƒ ) ≤ ( Icn )
( Ipƒ ) ≤ ( In )
( Ipƒ ) ≥ ( In )

The ( Icn ) of the circuit breaker is the maximum current the circuit breaker can safely disconnect . although it may then no longer be serviceable . to meet the requirements this value must be equal to or higher than the maximum fault current which may occur .
 
Q/As 2394 .

Which of the following is not a method for determining prospective earth fault current at the origin of an installation

Enquiry to the DNO
Direct measurement
Calculation using measured ( Ze ) and the supply voltage .
(d) Calculation using measured ( Zs ) and the supply voltage .

prospective fault current is measured to determine the maximum fault current which may occur , Any impedance measurement taken at the end of a circuit will be higher than that at the origin of the circuit , As a result the value obtained from the calculation in ( d ) is not going to produce the maximum value .
 
Gentlemen am Not downloading this for fun . Your Arse is on the line here . ( Time & Money ) Forewarned is forearmed

On your own Head 2394 / 5

Take Heed .. from C&Gs .. " Warning "

Answer that describes dangerous techniques and a heavy penalty will be applied to answers that describe invalid procedures

The installations being inspected and tested are generally energised , unless information is given to the contrary . ◄◄◄
As a result the need to isolate in order to carry out certain tests must be included in the test process . The description would generally need to include :

the need to obtain permission , to safety isolate and lock off and to retain the key .
A description of the actual safe isolation process would only need to be provided where expressly asked for in the Question .

This qualification relates to the periodic inspection of electrical installations and so encompasses the preparation , client discussion and the inspection , testing and reporting process , The testing process will include the need to confirm that test results are compliant with the requirements of BS-7671: Candidates will also need to identify non-compliances and award appropriate classification codes , Candidates will also be expected to identify the safety and practical aspects of periodic inspection .

Inspection:
The inspection process is a vital part of the periodic inspection process , many conditions may be identified during the inspection which would not be revealed by testing alone . Candidates are expected to be aware of the areas to be inspected , the actual items to be checked and the human senses to be Used whilst inspecting those items , Recording the outcome for each inspection item is also a requirement of the reporting process .

Candidates should be aware that the Schedule of inspections for the periodic inspection of installations provided in BS-7671: & GN-3 , together with the ( Examples of items requiring inspection given in BS-7671: , Appendix 6 ) provides detailed information on the items of inspection for these installations , Candidates should become familiar with the items they are to consider , inspect and record and this will greatly improve both their understanding of the inspection process and their success in any related questions .

( How to not screw UP ) ... Read the related Questions

Confirmation of compliance ; of the installation with the requirements of BS-7671: forms part of the periodic inspection process , The source document generally identifies that all testing is carried out at an ambient temperature of ( 20ºC ) This means that test values will not be at normal operating temperature and so this must be considered and where necessary compensated for .
 
Younger viewers . making you Aware , The answers are always in front of you . BS-7671:2011: & GN-3

Question Test Sheet
This paper relates to a " Closed book Exam " & therefore candidates should attempt the exam paper with no study-notes or text books .

Q) Minor Electrical Installation Work Certificate does not require a record of :
recap ; R/P.393. Your Q .

System earthing arrangements ... Part 2 : Installation details .
Departures , if any BS-7671:2008: ... Part 1 : Description of minor works
Method of fault protection ... Part 2 : Installation details .
Prospective fault current .
 
Younger viewers . Just knocked up this for an Example . Stretching it

A New installation is protected against faults by ( ADS ) When inspecting this method of protection , which of the following is not a essential check .

Your Q . Protective Conductors

a) Earthing conductor .
b) Circuit protective conductor(s)
c) Main protective bonding conductor(s)
d) Fire barriers

R/P.27 . Earthing Conductor is defined as “ A protective conductor connecting the Main Earthing Terminal of an installation to an earth electrode or to other means of earthing”

Protective conductors for Earthing are known as Circuit Protective Conductors (CPCs)
R/P.27 . Earthing : Connection of the exposed-conductive-parts of an installation to the main earthing terminal of that installation .

R/P.27 . Equipotential bonding is defined as: “ Electrical connection maintaining various exposed-conductive-parts and extraneous-conductive-parts at substantially the same potential ”

543.2.1. Types of Protective conductor .
A protective conductor may consist of one or more of the following :
(i) single - core cable
(ii) conductor in a cable .

542.4.1. In every installation a main earthing terminal shall be provided to connect the following to the ( Earthing conductor )
(i) The circuit protective conductor(s)
(ii) The protective bonding conductor(s)

recap ; R/P37 . Fig 2.1.

1 , 2 , 3 , 4 , Protective conductors .
Circuit protective conductor(s)
Main protective bonding conductor(s)
Earthing Conductor
4 .. Where required .
 
Principles , practices & Legislation for the periodic inspection of electrical installation . 2395-302 .

Written Examination

in this paper you will often be asked to provide longer answers for questions that ask you to " describe " or " explain " These are often related to inspection and / or test procedures and you are required to demonstrate your knowledge of the inspection and / or test process . ( 10 )

example ;
Describe , in detail , the procedure for carrying out a test to confirm , the continuity of the main protective bonding conductor connected to the water installation pipework .

there are a number of pointers in the question , The answer is worth 10 marks and the question asks for " detail " so a full description is required .

As this examination only considers periodic inspection , you can determine that the installation is energised , you would always need to confirm that it is safe to isolate the installation or circuit and state that safe isolation is carried out . On occasions the question may state that the permission to isolate has been given or safe isolation has been carried out

Such questions may also be preceded by a number of auxiliary questions relating to the actions required before or after the test concerned , in such cases these items would not need to be repeated in the procedure .

There is no such indication for this question and so the requirements must be included and so you will need to include obtaining permission and the isolation procedure in your description .

Option 1 ;
The answer could be provided as a description of the process in a " story " format , as in the following .

" " story format "
I would obtain permission from the client to isolate the installation , carry out safe isolation of the whole installation , lock off and retain the ( unique key ) I would then disconnect one end of the main protective bonding conductor . I would select a low-résistance ohmmeter , check condition and function , select a suitable long test lead and ( null the test leads ) , I would connect one test lead to the disconnected main protective bonding conductor and the other lead to the far end of the conductor , Test and record the results , I would then reconnect the main protective bonding conductor before reenergising the supply "

This answer and similar variations are perfectly acceptable and you would obtain the marks for the question , however , it does rely on the procedure being written down correctly the first time without missing any steps , it involves a considerable amount of writing and it is often difficult to spot any errors during the examination when you read back through your answer .

Option 2 ;
The answer can be structured as a set of bullet points .
• Obtain permission to isolate the supply
• Safety isolate , lock off and retain the key . PS unique key
• Disconnect the main protective bonding conductor at one end
• Select a low-résistance ohmmeter , check condition and function
• Select a suitable long test lead
• Null the test leads
• Connect the test leads to the disconnected bonding conductor and the far end .
• Test and record the result
• Reconnect the main protective bonding conductor before reenergising the supply

There is plenty of space to write down your answer . so you can leave a space between each bullet point , giving you the opportunity to add an additional line in later if you have missed a step in the process , you can also read through your answer much quicker and identify any omissions

Additional bullet points may be added at the end if you find you have missed out some information providing they identify when the action is carried out . for example if you find you have omitted to null the test leads the final bullet point could be added as ;

• Before carrying out the test the test leads should be nulled .

The second option , with the use of the bullets points , is generally quicker to complete , less prone to errors or omissions and clearly demonstrates your understanding of the test process , you can try both methods to find out which best suits you , however , Option 2 is strongly recommended .

it is important to recognise the need to carry out testing in a way that does not put yourself or anyone else at risk , also the test must be carried out in such a manner that produces valid results . No marks will be awarded for an answer that describes dangerous techniques and a heavy penalty will be applied to answers that describe invalid procedures .
 
What will be asked of You . 2394

Be able to test electrical installations prior to them being placed into service

You are required to be able to :
Select the test instrument(s) and their accessories for tests to include :

Continuity .
Insulation résistance .
Polarity .
Earth electrode résistance .
Earth fault loop impedance .
Prospective fault current .
RCD operation .
Phase sequence .
Functional testing .

Carry out tests in accordance with BS-7671: & GN-3 .
to include :
Continuity including
□ main protective bonding conductors'
□ circuit protective conductors'
□ ring final circuits
□ insulation résistance
□ polarity
□ external earth fault loop impedance (Ze)
□ system earth fault loop impedance (Zs) ... ( Z impedance , s system ) Zs
□ prospective fault current
□ RCD operation including additional protection
□ phase sequence
□ functional testing

Confirm compliance by verifying test results

Complete appropriate documentation in accordance with the BS-7671: GN-3 , including :
• Electrical Inspections Certificate
• Schedule of Inspections
• Schedule of Test results

Be able to commission electrotechnical systems and equipment .

You are required to be able to :
□ Clarify the commissioning procedures with relevant persons .
□ Carry out the commissioning of circuits , accessories and equipment to confirm functionality .
 

Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

thanks for the confirmation this is what i thought. i cant think of what use this device is . i have seen David Saverys Arc Fault Detection Device...
Replies
4
Views
392
  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top