Section 701. refer basic’s :icon_bs:
701.1. Scope .
This particular requirements of this section apply to the electrical installations in locations containing a fixed bath (bath tub, birthing pool ) or shower and to the surrounding zones as described in these regulations .
Summary of requirements
701 . Due to the presence of water, locations containing a bath or shower are onerous for equipment and there is an increased danger of electric shock .
• The additional requirements can be summarised as follows:
701.411.3.3. all low-voltage circuits serving location must be protected by 30mA RCDs .
701.411.3.3. all low-voltage circuits passing through zones 1 & 2 but not serving the location .
701.411.3.3. Additional protection by RCDs
Additional protection by the use of one or more RCDs having the characteristics specified in Regulation 415.1.1. shall be provided for low voltage circuits :
(i) serving the location .
(ii) passing through zone 1 and / or 2 not serving the location .
Note: See regulation 314.1. (iv) and 531.2.4. concerning the avoidance of unwanted tripping .
• Socket-outlets, e.g. BS-1363, are not allowed within 3 metres of zone 1 ( the edge of the bath or shower basin )
701.512.3.
Except for SELV socket-outlets complying with Section 414 and shaver supply units complying with BS-EN-61558-2-5.
socket-outlets are prohibited within a distance of 3m horizontally from the boundary of zone 1
• protection against ingress of water is specified for equipment within the zones . 0 , 1 , 2 .
701.512.2. External influences .
(i) In zone 0 : IPX7
(ii) In zone 1 and 2 : IPX4
This requirement does not apply to shaver supply units complying with BS-EN-61558-2-5. installed in zone 2 and located where direct spray from showers is unlikely .
Electrical equipment exposed to water jets. e.g. for cleaning purposes, shall have a degree of protection of at least IPX5 .
• there are restrictions as to where appliances, switchgear and wiring accessories may be installed.
701.512.3.
Erection of switchgear, controlgear and accessories according to external influences
The following requirements do not apply to switches and controls which are incorporated in fixed current-using equipment suitable for use in the zone or to insulating pull cords of cord operated switches .
701.512.3.
zone 0 .. switchgear or accessories shall not be installed . ( 0 is the plug hole )
zone 1
zone 2
701.55. Current-using equipment .
In zone 1 , only the following fixed and permanently connected current-using equipment shall be installed, provided it is suitable for installation in zone 1 according to the manufactures instructions :
- Whirlpool units
- Electric showers
- Shower pumps
- Equipment protected by SELV or PELV at a nominal voltage not exceeding 25V a.c. rms or 60V ripple-free d.c. the safety source being installed out zone 0 , 1 and 2 .
- Ventilation equipment
- Towel rails
- Water heating appliance(s)
- Luminaire(s)
701.1. Scope .
This particular requirements of this section apply to the electrical installations in locations containing a fixed bath (bath tub, birthing pool ) or shower and to the surrounding zones as described in these regulations .
Summary of requirements
701 . Due to the presence of water, locations containing a bath or shower are onerous for equipment and there is an increased danger of electric shock .
• The additional requirements can be summarised as follows:
701.411.3.3. all low-voltage circuits serving location must be protected by 30mA RCDs .
701.411.3.3. all low-voltage circuits passing through zones 1 & 2 but not serving the location .
701.411.3.3. Additional protection by RCDs
Additional protection by the use of one or more RCDs having the characteristics specified in Regulation 415.1.1. shall be provided for low voltage circuits :
(i) serving the location .
(ii) passing through zone 1 and / or 2 not serving the location .
Note: See regulation 314.1. (iv) and 531.2.4. concerning the avoidance of unwanted tripping .
• Socket-outlets, e.g. BS-1363, are not allowed within 3 metres of zone 1 ( the edge of the bath or shower basin )
701.512.3.
Except for SELV socket-outlets complying with Section 414 and shaver supply units complying with BS-EN-61558-2-5.
socket-outlets are prohibited within a distance of 3m horizontally from the boundary of zone 1
• protection against ingress of water is specified for equipment within the zones . 0 , 1 , 2 .
701.512.2. External influences .
(i) In zone 0 : IPX7
(ii) In zone 1 and 2 : IPX4
This requirement does not apply to shaver supply units complying with BS-EN-61558-2-5. installed in zone 2 and located where direct spray from showers is unlikely .
Electrical equipment exposed to water jets. e.g. for cleaning purposes, shall have a degree of protection of at least IPX5 .
• there are restrictions as to where appliances, switchgear and wiring accessories may be installed.
701.512.3.
Erection of switchgear, controlgear and accessories according to external influences
The following requirements do not apply to switches and controls which are incorporated in fixed current-using equipment suitable for use in the zone or to insulating pull cords of cord operated switches .
701.512.3.
zone 0 .. switchgear or accessories shall not be installed . ( 0 is the plug hole )
zone 1
zone 2
701.55. Current-using equipment .
In zone 1 , only the following fixed and permanently connected current-using equipment shall be installed, provided it is suitable for installation in zone 1 according to the manufactures instructions :
- Whirlpool units
- Electric showers
- Shower pumps
- Equipment protected by SELV or PELV at a nominal voltage not exceeding 25V a.c. rms or 60V ripple-free d.c. the safety source being installed out zone 0 , 1 and 2 .
- Ventilation equipment
- Towel rails
- Water heating appliance(s)
- Luminaire(s)