Bit big,the cutout,regarding IPXX etc
I am not sure wood boarding provides suitable containment in accordance with BS7671.does the wooden board not provide mechanical protection?
Will either use expanding fire proof foam foam or intumescent liningBit big,the cutout,regarding IPXX etc
The SWA is terminated to a metal box just behind the wooden board and the armour is earthedPersonally I am usually highly resistant to having concealed cable in commercial/industrial situations as I feel it must be accessible for inspection and testing. I also wonder how you will gland the SWA you are using? As you may know at least one end of the SWA must be earthed/terminated and connected with a fly lead to earth? How do you intend to seal the gaping hole?
It does there are many threads confirming thatI am not sure wood boarding provides suitable containment in accordance with BS7671.
The SWA is terminated to a metal box just behind the wooden board and the armour is earthed
I can cut a hole in the wood boad maybe. Thank you I will make it accessibleSo its inaccessible ................ not ideal
There is no issue with the wooden board and there is no issue with a rear entry tho. It all conforms to BS7671Why did the rear entry hole have to be butchered so big and would it not made sense to consider a fire rated material as a backing board/entry grommet such as Paxolin?