Are all the outgoing circuit RCBO protected?
All the circuits from the board i installed will be RCBO protected
I would of done as Adam posted with the incoming SWA if you have to have that meter at that position would have been a trunking down the RHS SWA made off at top end cap then T off like you have done for the meter.
 
Are all the outgoing circuit RCBO protected?

I would of done as Adam posted with the incoming SWA if you have to have that meter at that position would have been a trunking down the RHS SWA made off at top end cap then T off like you have done for the meter.
You would have made off the SWA to the end cap of the trunking?
 
How would a MCCB prevent such an event?
If there is a fault on one of the final circuits you would want the MCB to trip faster than the MCCB. A practical example of this I recall was one of the final circuits we installed the chippy put a nail through the cable now as we had a low ELI it took out the RCBO as well as the existing 50A MCB protecting this D.B. bad discrimination ( sorry selectivity new word)
 
If there is a fault on one of the final circuits you would want the MCB to trip faster than the MCCB. A practical example of this I recall was one of the final circuits we installed the chippy put a nail through the cable now as we had a low ELI it took out the RCBO as well as the existing 50A MCB protecting this D.B. bad discrimination ( sorry selectivity new word)
Trip faster? Does the MCCB not have to trip within 0.4s ?
 
If there is a fault on one of the final circuits you would want the MCB to trip faster than the MCCB. A practical example of this I recall was one of the final circuits we installed the chippy put a nail through the cable now as we had a low ELI it took out the RCBO as well as the existing 50A MCB protecting this D.B. bad discrimination ( sorry selectivity new word)
In that situation you would wanna substitute the 50A MCB for a type C or type D MCB?
 
0.4 sec under 32A and 5 sec over 32A
In the situation you describe surly a 50A type c or type D MCB would be the solution?
There's a small matter of short circuit capacity rating involved, here, mate.
 
Last edited:
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Birmingham

Thread Information

Title
Rear entry three phase board
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
66

Advert

Thread statistics

Created
Gigsy,
Last reply from
Gigsy,
Replies
66
Views
10,688

Advert

Back
Top