Smart Meter Tripping RCD | Page 2 | on ElectriciansForums
Discuss Smart Meter Tripping RCD in the UK Electrical Forum area at ElectriciansForums.net
Birmingham
Thought I would throw my tenant's problem regards Smart Meters (SM) into the mix, in the hope someone could maybe suggest what is going on?
May 2016 - tenants switch to E.org - no problem.
March 2017 - had Liberty 100 PAYG SM (top-Up via App) installed and immediately the RCD/fusebox starts tripping intermittently - every few hours, every day, after few days - see picture.
April 2017 - I contacted E.org and they stated that SM not cause switches to trip, fault is fusebox. Accept what they say.
Tripping continues and tenants check and monitor if appliances causing problem. None found.
BG electricians check home electrics 4 times and state domestic side and RCD all ok - Dec 2017, Aug 2018, Sept 2018 and Oct 2018.
After much elimination find Cause???!!!
Customer Top Up - when tenant tops up via app and then a few minutes later credit shows up on phone, then RCD immediately trips.
Supplier reading - after informing E.org about above and they do On Demand reading from their end, then RCD immediately trips.
E.org change SM Oct 2018 and tripping now worse.
BG check after SM change and state domestic side and RCD all ok.
E.org state that fault is RCD as have changed SM and thus are insistent they are not at fault.
BG believe it is SM, so I am between a rock and hard place.
Requested E.org replace SM with Dumb Meters as a way of eliminating or confirming SM is cause of tripping, but will only do if I pay.
Now starting case with Energy Ombudsman… And tenants’ life not good as now 3/4 times a day have to reset RCD.
Any ideas/advice?
[ElectriciansForums.net] Smart Meter Tripping RCD
I have asked E.org what the mobile phone signal strength is when they installed the 1st and 2nd SM. The house is in a poor signal area. Would the need to boost the signal from the SM cause interference in the CU?
Will get tenant to take pic when next trip.
This is a situation crying out for more in-depth testing,including data logging,etc.
I hold minimal faith,in BG being capable of delivering this...
4 electrical checks - 3 by BG, last one by PH Jones.
What exactly regarding in depth checks are needed, so I can request these be made.
I feel responsible for tenant, as not fair they are living with RCD tripping constantly, and who knows how long Energy Ombudsman get to resolution, 8 weeks, after xmas!
As far as I know, mobile modems vary their signal strength based on the strength of the signal they receive, so if the signal is weak, they'll increase their output accordingly.
Yup, the weaker the signal the more power the send out trying to get good comms with the local mast.
Even if there is a neutral-earth fault downstream, there would still be no leak as long as there is no potential difference between earth and neutral.
If there was a neutral earth fault downstream e.g. shorted together then there would indeed be no PD but there would be earth leakage, it will parrallel the neutral return current through the cpc. If RCD protected then that would trip from the L-N inbalance
To be fair, I think the BG spark has done what he can. He has taken Zs to prove effective connection to earth. He has taken IR at 250vdc. He likely selected 250vdc so he could test with loads connected to eliminate both wiring and loads for earth faults. Sensible. He has also ramp tested RCD.
I agree with others that it may well be interference from meter comms mobile being so close to RCD. IIRC the RCD in that board will be an MEM with a functional earth wire it may act like an antennae!
Hi - From afar I guess we can never solve this, but there are couple more things for an Electrician to look at in my view. Did the BG Electrician actually personally observe the remote test and the tripping RCD? I would be seeking cooperation from the meter company with some more testing. Something like : Standing at the box with main switch, RCD and all circuits on, have the remote test done and observe the RCD trip. Reset RCD and turn all MCBs off and repeat the remote test and observe any trip. Safely remove the outgoing N from the RCD (still leaving all MCBs off) and repeat the remote test and observe any trip.
You need to find someone with an electromagnetic radiation tester to see what the meter output is.
Reply to Smart Meter Tripping RCD in the UK Electrical Forum area at ElectriciansForums.net
Happens on every job of ours, houses are usually empty for a year or so and they are always ÂŁ300-ÂŁ400 in debt mostly due to the standing charge...
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...