Hi all right the socket is on a ring final then going to the 1st sfcu then looping out to the 2nd sfcu o know you can only have 1 socket off a spur but both sfcu will be at 3a so i don't think i need a sfcu by the socket.
Maybe taffy was thinking that way too which would explain why he said 26a could be drawn, however just going by the ops drawing there is nothing to suggest it would be looped through so in my opinion it was worth 5 pages just to clarify the point that,
yes his circuit is correct providing he wires from the load side of the fcu and not looping from the feed.
Everybody happy with the clarification now?
Maybe taffy was thinking that way too which would explain why he said 26a could be drawn, however just going by the ops drawing there is nothing to suggest it would be looped through so in my opinion it was worth 5 pages just to clarify the point that,
yes his circuit is correct providing he wires from the load side of the fcu and not looping from the feed.
Everybody happy with the clarification now?
First drawing isn't wrong though as its designed on 6amp max load, the OP should label up max fuse size that should be replaced if it blows in future. But on saying that i do see where Taffy is coming from now and i do agree that if the fuses were replaced with 13a ones then this would show an overload of the cable.