Hi all is this ok to run two sfcu like this ?

[ElectriciansForums.net] Spur with two sfcu on it
Or should i run it like this
[ElectriciansForums.net] Spur with two sfcu on it
 
Sorry Taffy you lost me on that one i don't see any difference at all Appendix 15 shows spur protecting sockets? You dont need a FCU protecting a FCU where would it end?

Ok, the part of the diagram on page 425 shows a spur off the ring main at 9 oclock. The 13A FCU is limiting the current that can flow through to 13A therefore protecting the cable. The OP diagram 1 shows a spur going straight to the first FCU and then on to another FCU. Therefore with 13A fuses put in each it is possible that the total draw could be 26 Amps thus overloading the cable. The 3 amp fuses fitted to the FCU`s are irrelevant as they are protecting the cable going out from the FCU to the appliance.

Now I appreciate that 6 amps, or the load from a boiler and a light (which is going to be less in all likleyhood) is not going to damage the supply cable however the light and the boiler are " fixed equipment" therefore the relevant part of the diagram is at 6 oclock where only 1 fixed item is allowed.

The reasoning for this reg IMHO is that should the fixed equipment be changed in the future, say an immersion for a boiler and a socket for the FCU running the light then you have an overloaded cable.

I refer to my previous post regarding fixed equipment on spurs.
 
Ok, the part of the diagram on page 425 shows a spur off the ring main at 9 oclock. The 13A FCU is limiting the current that can flow through to 13A therefore protecting the cable. The OP diagram 1 shows a spur going straight to the first FCU and then on to another FCU. Therefore with 13A fuses put in each it is possible that the total draw could be 26 Amps thus overloading the cable. The 3 amp fuses fitted to the FCU`s are irrelevant as they are protecting the cable going out from the FCU to the appliance.

Now I appreciate that 6 amps, or the load from a boiler and a light (which is going to be less in all likleyhood) is not going to damage the supply cable however the light and the boiler are " fixed equipment" therefore the relevant part of the diagram is at 6 oclock where only 1 fixed item is allowed.

The reasoning for this reg IMHO is that should the fixed equipment be changed in the future, say an immersion for a boiler and a socket for the FCU running the light then you have an overloaded cable.

I refer to my previous post regarding fixed equipment on spurs.

I actually think this is an interesting debate and it has got me thinking TBH. I think Taffy is right here. The 13 amp FCU protects the whole of this spur cable in the future no matter what DIY Dan adds to it (and he will). The FCU's downstream could allow 26 amps to be pulled through and damage the spur cable upstream. Hmm
 
Last edited by a moderator:
Ok, the part of the diagram on page 425 shows a spur off the ring main at 9 oclock. The 13A FCU is limiting the current that can flow through to 13A therefore protecting the cable. The OP diagram 1 shows a spur going straight to the first FCU and then on to another FCU. Therefore with 13A fuses put in each it is possible that the total draw could be 26 Amps thus overloading the cable. The 3 amp fuses fitted to the FCU`s are irrelevant as they are protecting the cable going out from the FCU to the appliance.

Now I appreciate that 6 amps, or the load from a boiler and a light (which is going to be less in all likleyhood) is not going to damage the supply cable however the light and the boiler are " fixed equipment" therefore the relevant part of the diagram is at 6 oclock where only 1 fixed item is allowed.

The reasoning for this reg IMHO is that should the fixed equipment be changed in the future, say an immersion for a boiler and a socket for the FCU running the light then you have an overloaded cable.

I refer to my previous post regarding fixed equipment on spurs.

I get it now. That and what ipf explained. It'd be best to incorporate the spur as part of the ring or put the 13a spur in.


We only do new builds or complete refurbs when we do domestic, the rest is commercial work and in both circumstances I'm supervised. Always learning and even thou this wasn't my post I learned something today.

Sorry to bore you ez and biff. Was there nothing else on the forum you could've read??
 
Last edited by a moderator:
Either option would be ok unlimited outlets allowed as the first fcu limits the total draw to 13a from that leg of the ring

That's what I was thinking at first but if second spur was connected to supply side of first spur then it would be wrong.

Why is everyone getting uptight about this?? It's Sunday..... Chill day
 
No it's not your right it's fused at 3a which still makes the circuit correct
everything from the fcu in picture one is limiting the draw to 3a

OK but he stated it would be "looped". I take it that means the second FCU is fed from the supply of the first FCU and not the load side. That would mean the 3 amp fuse would protect the light and not the spur cable and that the second FCU could draw up to 13 amps?? That's my take on it but I may have read it wrong.
 
Yes but then the circuit wouldn't be wired correctly so not a design fault, not uptight about it but to say the circuit is wrong is not true, it may not be ideal or suitable for the use intended but it is correct as far as design goes, outlets are unlimited from fcu taken from the ring as the fcu be it 3,5,13a will limit the loading from the leg to the rating of the fuse. :)

As PP says above looping would be incorrect but ops original post was just a block diagram
 
Last edited by a moderator:
Not saying you was uptight....but there was a few others.... I never said pic 1 was wrong but I came round to taffys way of thinking.

I can't remember seeing he was going to loop the fcu's I may have read it wrong too
 
Maybe taffy was thinking that way too which would explain why he said 26a could be drawn, however just going by the ops drawing there is nothing to suggest it would be looped through so in my opinion it was worth 5 pages just to clarify the point that,
yes his circuit is correct providing he wires from the load side of the fcu and not looping from the feed.

Everybody happy with the clarification now?
 
Last edited by a moderator:
Maybe taffy was thinking that way too which would explain why he said 26a could be drawn, however just going by the ops drawing there is nothing to suggest it would be looped through so in my opinion it was worth 5 pages just to clarify the point that,
yes his circuit is correct providing he wires from the load side of the fcu and not looping from the feed.

Everybody happy with the clarification now?

Another pint please barman
 

Reply to Spur with two sfcu on it in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Thank you everyone for your comments Celia
Replies
6
Views
446
  • Question
It can be easy to lose the sequence of things. If the fused spur has a neon indicator and this isn’t coming on then I wonder if -the original...
Replies
6
Views
607
hI Gent's. I I can explain this spur line briefly, maybe someone can help me? Everything is Spur, no rings. Inside of the house and main fuse...
Replies
0
Views
234
  • Solved
Please use the like button to thank, like or whatever. As the forum treats that as a positive message then and uses it to score members.
    • Optimistic
Replies
11
Views
865
  • Question
The pics you put up of the consumer unit are all good .....all circuits RCBO protected and as above swap the fuse out for a 3 amp
Replies
2
Views
497

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks