All this chatter for installing a couple of points , you'd think domestic work is complex reading all this lol.
Sorry Taffy you lost me on that one i don't see any difference at all Appendix 15 shows spur protecting sockets? You dont need a FCU protecting a FCU where would it end?
Really makes you wonder what's going on out there!
very little if it takes hours of debate to fit 2 fcu's :-D
Ok, the part of the diagram on page 425 shows a spur off the ring main at 9 oclock. The 13A FCU is limiting the current that can flow through to 13A therefore protecting the cable. The OP diagram 1 shows a spur going straight to the first FCU and then on to another FCU. Therefore with 13A fuses put in each it is possible that the total draw could be 26 Amps thus overloading the cable. The 3 amp fuses fitted to the FCU`s are irrelevant as they are protecting the cable going out from the FCU to the appliance.
Now I appreciate that 6 amps, or the load from a boiler and a light (which is going to be less in all likleyhood) is not going to damage the supply cable however the light and the boiler are " fixed equipment" therefore the relevant part of the diagram is at 6 oclock where only 1 fixed item is allowed.
The reasoning for this reg IMHO is that should the fixed equipment be changed in the future, say an immersion for a boiler and a socket for the FCU running the light then you have an overloaded cable.
I refer to my previous post regarding fixed equipment on spurs.
Ok, the part of the diagram on page 425 shows a spur off the ring main at 9 oclock. The 13A FCU is limiting the current that can flow through to 13A therefore protecting the cable. The OP diagram 1 shows a spur going straight to the first FCU and then on to another FCU. Therefore with 13A fuses put in each it is possible that the total draw could be 26 Amps thus overloading the cable. The 3 amp fuses fitted to the FCU`s are irrelevant as they are protecting the cable going out from the FCU to the appliance.
Now I appreciate that 6 amps, or the load from a boiler and a light (which is going to be less in all likleyhood) is not going to damage the supply cable however the light and the boiler are " fixed equipment" therefore the relevant part of the diagram is at 6 oclock where only 1 fixed item is allowed.
The reasoning for this reg IMHO is that should the fixed equipment be changed in the future, say an immersion for a boiler and a socket for the FCU running the light then you have an overloaded cable.
I refer to my previous post regarding fixed equipment on spurs.
First pic a no go, second pic correct.
not sure why this has got to fourth page.
Either option would be ok unlimited outlets allowed as the first fcu limits the total draw to 13a from that leg of the ring
Said my piece Pic 1 is wrong, bored now.
Either option would be ok unlimited outlets allowed as the first fcu limits the total draw to 13a from that leg of the ring
No it's not your right it's fused at 3a which still makes the circuit correct
everything from the fcu in picture one is limiting the draw to 3a
Hi all right the socket is on a ring final then going to the 1st sfcu then looping out to the 2nd sfcu o know you can only have 1 socket off a spur but both sfcu will be at 3a so i don't think i need a sfcu by the socket.
Maybe taffy was thinking that way too which would explain why he said 26a could be drawn, however just going by the ops drawing there is nothing to suggest it would be looped through so in my opinion it was worth 5 pages just to clarify the point that,
yes his circuit is correct providing he wires from the load side of the fcu and not looping from the feed.
Everybody happy with the clarification now?