today i have a fault that is driving me crazy. new installation - barn conversion
end of overhead lines, transformer in garden serving 3 properties, this one has a new underground cable from pole to new cutout and has
been left on TT by dno (originally a temp supply)
i have a 2 way ccu with 2x rcbos, each serving a submain on 16mm t/e +10mmearth to a main switch / mcb board at each end of the barn (its huge!)
one end behaves perfectly
the other has a strange fault.
with everything on EXCEPT the hob and cooker isolators the installation has been running fine for weeks.
turn either of the above on and out goes the rcbo.. easy yes ?? dodgy new appliance??? NO
as with the rest of the installation off at each mcb, they run fine, flat out .then connect back in a lighting circuit that was otherwise fine (running for
3 weeks) and out goes rcbo :*( same if i connect in heating system, or insert a plug in socket tester!
rcbos test out fine
IR of entire installation is spot on, mostly clear, worst reading was 12mohm on said lighting circuit which rises to clear after a few secs
L-PEN at incomer is 0.18ohm (i put pme link in made no difference) current Ze as still TT is only 2ohm as it wet and transformer in the garden is only 10m away
whats going on!!!!!!
end of overhead lines, transformer in garden serving 3 properties, this one has a new underground cable from pole to new cutout and has
been left on TT by dno (originally a temp supply)
i have a 2 way ccu with 2x rcbos, each serving a submain on 16mm t/e +10mmearth to a main switch / mcb board at each end of the barn (its huge!)
one end behaves perfectly
the other has a strange fault.
with everything on EXCEPT the hob and cooker isolators the installation has been running fine for weeks.
turn either of the above on and out goes the rcbo.. easy yes ?? dodgy new appliance??? NO
as with the rest of the installation off at each mcb, they run fine, flat out .then connect back in a lighting circuit that was otherwise fine (running for
3 weeks) and out goes rcbo :*( same if i connect in heating system, or insert a plug in socket tester!
rcbos test out fine
IR of entire installation is spot on, mostly clear, worst reading was 12mohm on said lighting circuit which rises to clear after a few secs
L-PEN at incomer is 0.18ohm (i put pme link in made no difference) current Ze as still TT is only 2ohm as it wet and transformer in the garden is only 10m away
whats going on!!!!!!