Yes, no different to using a split load board, as found in thousands of installations.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Stange fault on new installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have 12 years experience, have relevant courses and part p all done properly but im not here to justify that
i would have fitted a dual rccb board at scource but did this to reduce long runs, there are socket outlet and lighting curcuits on each board serving both floors so you dont loose all sockets on say ground floor because of 1 rcbo tripping. Same goes for lights Maybe i hadn't explained that well because the circuits are spread well accross the ccu's.
I was of the understandig that a type s 100ma rcd was required on swa on a tt installation but if i am wrong please tell me?
I will be checking leakage next week, untill then theres nothing more we can discuss really so thanks all for initial advice
Murdoch, thats how I read it.no, he is saying that each sub main and board are protected by a RCBO at source! So when the RCBO trips, the entire wing goes off
Wasn't aware that the installation is TT.
As such the installation will either require a very low earth electrode resistance or RCD protection at source.
The OP has used RCBOs, which I doubt are time delayed.
The OP has split the installation across two RCBOs to ensure that if one trips, not all power and lighting is lost.
The OP has a fault which could be due to cumulative earth leakage.
Don't really understand why some members are slagging the OP off?
Yes the OP should have used 100mA s type RCDs up front, but construction methods require 30mA instead.
Note to OP, mechanical protection is not required to be earthed.
today i have a fault that is driving me crazy. new installation - barn conversion
end of overhead lines, transformer in garden serving 3 properties, this one has a new underground cable from pole to new cutout and has
been left on TT by dno (originally a temp supply)
i have a 2 way ccu with 2x rcbos, each serving a submain on 16mm t/e +10mmearth to a main switch / mcb board at each end of the barn (its huge!)
one end behaves perfectly
the other has a strange fault.
with everything on EXCEPT the hob and cooker isolators the installation has been running fine for weeks.
turn either of the above on and out goes the rcbo.. easy yes ?? dodgy new appliance??? NO
as with the rest of the installation off at each mcb, they run fine, flat out .then connect back in a lighting circuit that was otherwise fine (running for
3 weeks) and out goes rcbo :*( same if i connect in heating system, or insert a plug in socket tester!
rcbos test out fine
IR of entire installation is spot on, mostly clear, worst reading was 12mohm on said lighting circuit which rises to clear after a few secs
L-PEN at incomer is 0.18ohm (i put pme link in made no difference) current Ze as still TT is only 2ohm as it wet and transformer in the garden is only 10m away
whats going on!!!!!!
(b) for every circuit. Other than at the origin of the installation, every circuit or group of circuits that may have to be isolated without interrupting the supply to other circuits should be provided with its own isolating device. The device must switch all live conductors in a TT system and all line conductors in a TN system.
(b) for every circuit. Other than at the origin of the installation, every circuit or group of circuits that may have to be isolated without interrupting the supply to other circuits should be provided with its own isolating device. The device must switch all live conductors in a TT system and all line conductors in a TN system.
Who said anything about faults !There is a difference between isolation and fault protection!
537.2.1.1
Who said anything about faults !
The RCBOs provide fault protection. They can be used for isolation, though in TT installations they would require to be double pole. Isolation however can be achieved by using the main switch which is required to be double pole.537.2.1.1
Who said anything about faults !
So thats part (a) 537.1.4 sorted then at the origin.The RCBOs provide fault protection. They can be used for isolation, though in TT installations they would require to be double pole. Isolation however can be achieved by using the main switch which is required to be double pole.