>richy3333 - It's no different to a dual rcd protected property, as i say i was trying to reduce my final curcuit runs

>tony mc - The incoming ccu houses a wilex 100A main switch and 2x wilex 50A 30mA single pole RCBO's.


I have to disagree with you on that point. You would never put the downstairs sockets and lights on the same RCD would you?
 
Hi

I might be missing something here with your reply in post 15

IF it does turn out to be cumulative earth leakage i will have to expose the short vertical run in the stud wall and install some earthed mechanical protection, and fit a pair of rcd's into the consumer units.

If it is just overall leakage getting rid of the RCBO and placing one RCD in each of the CU is replicating exactally what you have now as far as the RCD is concerned re leakage!
 
By splitting the house left and right across 2 RCDs you have meant your installation is not compliant with the regs.

Read part 9 again.
 
Jeesus any need for that? As stated in post #1 the installation is TT so i would need some sort of RCD at the scource anyway even with SWA I'd need type S 100mA. Yes there would be discrimination but still could go out loosing the whole house.

IF it does turn out to be cumulative earth leakage i will have to expose the short vertical run in the stud wall and install some earthed mechanical protection, and fit a pair of rcd's into the consumer units.

Apologies if I have hit a nerve. If you want a cuddle you're on the wrong forum, but it sounds like you might be well out of your depth to me. No offence, but someone (a customer) is paying for this.

Would you care to state your qualifications and experience? The forum might be a place for advice but its not a substitute for correct/adequate training and experience.

BTW whilst I am not against an upfront 100mA RCD on a TT system can you please quote the Reg that requires it?
 
I have 12 years experience, have relevant courses and part p all done properly but im not here to justify that

i would have fitted a dual rccb board at scource but did this to reduce long runs, there are socket outlet and lighting curcuits on each board serving both floors so you dont loose all sockets on say ground floor because of 1 rcbo tripping. Same goes for lights Maybe i hadn't explained that well because the circuits are spread well accross the ccu's.

I was of the understandig that a type s 100ma rcd was required on swa on a tt installation but if i am wrong please tell me?

I will be checking leakage next week, untill then theres nothing more we can discuss really so thanks all for initial advice
 
i have a 2 way ccu with 2x rcbos, each serving a submain on 16mm t/e +10mmearth to a main switch / mcb board at each end of the barn (its huge!)

So you have 30mA RCBO's at source AND dual 30Ma RCD boards at each end of the property?

If this is the case, and the hob / oven are on separate RCD's, then I would suggest you've got the neutrals mixed up!

Or have I mis-understood your design and installation?

Just saying
 
Hold up, it's quite common to split houses front to back or side to side, and to have a mixture of light and power on each RCD.
That way if an RCD does trip, not all the lights will go off.
 
Hold up, it's quite common to split houses front to back or side to side, and to have a mixture of light and power on each RCD.
That way if an RCD does trip, not all the lights will go off.

But in this case he sounds like he has 30mA RCBO's protecting dual RCD board - one at each end of the property - so if this is the case not only does he have 2 x 30mA in series, and the fact that the RCBO's will 99% of the time trip out before the RCD on the sub board - turning off all the power to the "wing" of the building
 
no rccb's in the sub boards those are main switch + mcbs sorry for being about as vague as humanly possible, if i could draw a diagram that would explain better.

either way im going to pin point the leakage next week, and if needs be i will protect the short bit of 16mm t/e in the wall. Remove upfront rcbo's and fit dual rcd boards in each wing as 4 rccbs then should allow for this leakage if it is indeed the appliances!
 
no rccb's in the sub boards those are main switch + mcbs sorry for being about as vague as humanly possible, if i could draw a diagram that would explain better.

either way im going to pin point the leakage next week, and if needs be i will protect the short bit of 16mm t/e in the wall. Remove upfront rcbo's and fit dual rcd boards in each wing as 4 rccbs then should allow for this leakage if it is indeed the appliances!


Ok. Have you got an earth leakage clamp meter?
 
Must be missing something then?
Post #19 states that if the fault is due to cumulative leakage then the OP will have to install earthed mechanical protection and fit a pair of RCDs into the consumer units.
Seems to be saying that there are no RCDs in the CUs at present?
 
Must be missing something then?
Post #19 states that if the fault is due to cumulative leakage then the OP will have to install earthed mechanical protection and fit a pair of RCDs into the consumer units.
Seems to be saying that there are no RCDs in the CUs at present?

no, he is saying that each sub main and board are protected by a RCBO at source! So when the RCBO trips, the entire wing goes off
 

Reply to Stange fault on new installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
454
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Cheers guys. I was working on the same assumption, but was aware for MF the wagos in wago box were derated 32s, and couldn't find anything to...
Replies
7
Views
272
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top