Not sure where you are going with the old stuff, but most older TT installations have double pole rcd's or more than one CU. I'm trying to go to the place where you understand that the requirement for double pole isolation does not equate to a requirement for double pole protective devices. I haven't said that protective devices need to be double pole on TT. But they must be DP if used as isolators which they would be in this installation.
The problem is the op has designed/upgraded this install with single pole devices where they should be double pole.
Again there is no requirement for double pole protective devices. Again no but when used as isolators.
The whole design is a dogs dinner but he should be putting that part to current standards at least.
Yes there are problems with the installation, but as far as I am aware it complies with the requirements of BS7671! Again you can't use SP RCBO to isolate a circuit in TT system.