Evening all..

I am currently doing my first full rewire. The customer is having the wall knocked down with the meter/cutout and CU on it. the plan was to move the CU under the stairs and get DNO to move the supply to the same place. They have said they cannot move the cutout to where the CU will be. The approx length from cutout to CU will now be around 8m so I need to add a fused switch. My questions are about which type of cable to use:

1. I could use 2 core 25mm SWA (seperate 16mm earth) but I am unsure of how easy this is to bend through the route? It will be going straight up from the meter box and then 90degress into the house wall entering directly under the first floor floorboards. What is the best way to get it through the wall without putting too much strain on it (with regards bending angle)?

2. BS7671 states 25mm to be used, however I am fusing down to 80A, could I not use 16mm SWA as CCC is 87A?

3. Could I use tails as at no point will the tails be buried in the wall. They will be going directly under the floor boards from outside the house (suitable protected outside) and then down from the ceiling directly behind the new CU (there will be a cavity behind new CU as I will bring out from the wall). Do they need to be protected if they are not getting buried in the wall?

4. Which is easier to move around/use T&E (16mm or 25mm), SWA (16mm or 25mm) or tails?

5. Which is the best fused switch to use? KMF, wylex metal? Can I gland SWA into a KMF or does it need an adaptable box?

Cheers chaps:biggrin:
 
Interesting discussion on discrimination, a question I've asked myself before, and received conflicting replies.

The meter box belongs to the owner of the property, but the DNO has certain requirements; BS 8567 (gas is BS 8499).

I asked my DNO (SSE) before on what they would expect to see in such a situation, as here. I asked DNO what would they say about extended tails, 'We would expect a switch fuse, as it is a submain'. Could I put equipment in said box, answer 'No not really, what are you thinking of? Switch fuse? 'Ahhh, okay'.

Considering size of fuse in switch fuse (i.e. DNO 100a, switch fuse 80a), I asked Elecsa tech support for advice;

'Without referring to the time current characteristics of each device for the exact information we believe that the fault protection characteristics of each device will be similar but not the same.

They do provide fault and overload protection for the whole installation. Therefore there will certainly some discrimination with overload protection.

The final decision regarding the discrimination of the two devices would be down to the designer of the installation'.
 
might be an idea to use a MCCB instead of a sw.fuse. cost permitting. this should ensure the MCCB tripping before the \DNO fuse. discuss?
 
might be an idea to use a MCCB instead of a sw.fuse. cost permitting. this should ensure the MCCB tripping before the \DNO fuse. discuss?

Mccb would clearly take out the supply before dno fuse. Domestically 80A is usially suffiecent but with some customers adding multiple electric showers and u/floor leccy heating they are demanding alot more. Had a call out last winter where customers off supply, dno fuse on the pole had gone 60A on pole, 80A in dno head 80A switch fuse! They replaced it with 80.
 
Waw have you really installed another meter box next to dno box! If you have that is shocking imo. Put ur switch fuse in the dno box, if its on. The owners property its theirs not dno so you may add your sw fuse in there! Flobbogasted at that pic!!

Box on the right houses the gas meter you wally !
 

Reply to SWA, T&E or tails?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
581
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
768
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
864
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
615

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top