Discuss TN-S & TT on same installation what should I class it as? in the UK Electrical Forum area at ElectriciansForums.net
it looks all leathered where its bent...Gas feed to cooker through to other room
Yep aggree as however PFC could be as high and should not 16Ka on a 230 supply as per OSG page 70 As said May be high so a measure to ensure devices meet capasityI doubt he will have any higher than 3-4Ka maximum, even if he's near the Dno tx.
It is simply a TN-s system period as you have a suppliers earth as your primary earth. The Earth rod is purely that and is not and should not be translated as a TT system. The earth rod is there as a belt and braces job and to provide and give a better earth path only. The only issue you may have is a PFC as with the very low resitance to earth you will possibly get a very high Earth Fault current exceeding the Ka of your protective device/devices. Your short circuit fault current will be considerably lower. In Compex installation the better the earthing arrangement - and in design additional earth rods are by design placed in the installation for greater protection. Why remove it as its offering a good additional earth path - doing its job.
Reply to TN-S & TT on same installation what should I class it as? in the UK Electrical Forum area at ElectriciansForums.net