TNCS High ZE at origin | on ElectriciansForums
Guest viewing is limited

Discuss TNCS High ZE at origin in the UK Electrical Forum area at ElectriciansForums.net

A

AdamGiguere

Hi there

Testing at origin of a domestic property, I have found:

L-N: 0.44 Ohms
L-E: 9.89 Ohms

I had the DNO attend clients address, there response was that it was quite high and confirmed readings of 0.44 for ZE. (Pleasee attached document with their response)

My concern is they don't seem to have checked the reading between L-E......

Anyone know what could be the cause of this? MET connections are tight and in good condition....

Many thanks in advance.

Adam

[ElectriciansForums.net] TNCS High ZE at origin
 
They haven't mentioned about the L-E reading which is why I'm a little concerned as I'm aware the highest should be recorded....

But in any case the L-N and L-E readings should be more or less the same for TNCS...

I'm just wondering what could be the cause of the high ZE on L-N...

The only thing I can think of is the earthing connection could be damaged somewhere.

Perhaps an earth rod would fix.
 
They have mentioned this yes, however any board I test L-E at I get Ze of about 9 ohms, the same as when I test Ze at end of circuits I get 9 ohms.

I will call them tomorrow but I'm sure they'd have checked both L-N & L-E surely.

If so why am I getting 9 ohms...baffling me...
 
They have mentioned this yes, however any board I test L-E at I get Ze of about 9 ohms, the same as when I test Ze at end of circuits I get 9 ohms.

I will call them tomorrow but I'm sure they'd have checked both L-N & L-E surely.

If so why am I getting 9 ohms...baffling me...
well it's the pen conductor getting tested so if your testing at the consumer unit L-E it would be the same result more or less as testing L-N unless the earth connection going into the cut out needs attention giving you a high impedance
 
Reading the OP note from DNO, they have provided PME at 0.44 Ohms. They expect the Electrician to connect to the new PME tail and confirm you now have Ze of 0.44 and that it is sufficient to meet ADS in the installation.
Have you done that?

Stuggling with their wording and action to be taken. When they say

When they say provide new PME tails what do they mean exactly...?
 
well it's the pen conductor getting tested so if your testing at the consumer unit L-E it would be the same result more or less as testing L-N unless the earth connection going into the cut out needs attention giving you a high impedance

When you say the "cut out" what do you mean?

Understand the N and E are one in the same more or less but need to sign off the work but at each point measuring Ze (L&E) it's far to high -
 

Reply to TNCS High ZE at origin in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
911

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top