Hi there

Testing at origin of a domestic property, I have found:

L-N: 0.44 Ohms
L-E: 9.89 Ohms

I had the DNO attend clients address, there response was that it was quite high and confirmed readings of 0.44 for ZE. (Pleasee attached document with their response)

My concern is they don't seem to have checked the reading between L-E......

Anyone know what could be the cause of this? MET connections are tight and in good condition....

Many thanks in advance.

Adam

[ElectriciansForums.net] TNCS High ZE at origin
 
I cannot see anywhere that it states that the property is currently a PME system. In fact, the OP says “the 25mm earth comes from elsewhere - I'll have to investigate further” so it looks like it is currently a TT or TNS system. The DNO actually seem to be saying they made a decision to provide PME tails for an electrician of choice to connect into the excising setup. I suspect they have not done this yet and will do the actual conversion when an electrician is present.

Are you sure this is not a TT system?

Hi Davisonp

This sounds like a good translation of their wording.

I'm pretty sure it's not a TT system/although could be mistaken.

I did think perhaps maybe a TNS due to the 0.44 on the L-N

But have been advised by a colleague who came to site with me originally that it's a TNCS.

Hopefully they have a log of their visit and can advise what system it definitely is
 
I thought it was only myself that was confused so i refrained from posting anything
Having read the later replies it appears to me I am not alone

Op,can you give a definitive description of the head and the supply type
Is there a separate earth conductor entering the property?

Can you confirm or deny a installation earthing conductor connection has been made
to the Pme at the cut out or elsewhere even?
 
I thought it was only myself that was confused so i refrained from posting anything
Having read the later replies it appears to me I am not alone

Op,can you give a definitive description of the head and the supply type
Is there a separate earth conductor entering the property?

Can you confirm or deny a installation earthing conductor connection has been made
to the Pme at the cut out or elsewhere even?

Will retrieve pics and post ASAP...I've asked the tenant (family friend) to take a pic or two of the meter cupboard
 
If there was no link - would I be getting a reading similar to 9 ohms?

I'd expect no reading...?

If so and there is no link - where is the 9 ohms coming from?
We need a clearer picture of what is going on because this has become very confused. I think I wrongly assumed the earthing conductor was connected to the head hence my assumption there was no link to this conductor from the supply neutral.
 

Reply to TNCS High ZE at origin in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
911

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top