A

AdamGiguere

Hi there

Testing at origin of a domestic property, I have found:

L-N: 0.44 Ohms
L-E: 9.89 Ohms

I had the DNO attend clients address, there response was that it was quite high and confirmed readings of 0.44 for ZE. (Pleasee attached document with their response)

My concern is they don't seem to have checked the reading between L-E......

Anyone know what could be the cause of this? MET connections are tight and in good condition....

Many thanks in advance.

Adam

[ElectriciansForums.net] TNCS High ZE at origin
 
The cut out does not come with the earth brass bar as shown above the 25mm earth comes from elsewhere - I'll have to investigate further.

As there must be a problem with the earthing connection?

Just baffling as to why the DNO have not picked this up, would they have just done the test between L-N?

Surely not?
 
Not of the origin - I should have. Apologies...

I'll question the DNO tomorrow when I call.

I'll have to return to the site. There must as you mentioned be something wrong with the earth connection but I couldn't for the life of me see anything wrong earlier when I was looking....
 
If they are telling you it is PME and you are getting those readings then you have no link between the earthing conductor and supply neutral.

Yes that's what it would seem right.

There must be a problem with the link but just wondering why the DNO have not picked this reading up....?

Would they have just tested between L-N ?
 
Yes that's what it would seem right.

There must be a problem with the link but just wondering why the DNO have not picked this reading up....?

Would they have just tested between L-N ?
Hi - from their wording, they have provided you with a PME means of earthing. However given the 9 Ohms Ze, it seems it's not been connected to the installation's MET (by you :) )
 
I cannot see anywhere that it states that the property is currently a PME system. In fact, the OP says “the 25mm earth comes from elsewhere - I'll have to investigate further” so it looks like it is currently a TT or TNS system. The DNO actually seem to be saying they made a decision to provide PME tails for an electrician of choice to connect into the excising setup. I suspect they have not done this yet and will do the actual conversion when an electrician is present.

Are you sure this is not a TT system?
 
I cannot see anywhere that it states that the property is currently a PME system. In fact, the OP says “the 25mm earth comes from elsewhere - I'll have to investigate further” so it looks like it is currently a TT or TNS system. The DNO actually seem to be saying they made a decision to provide PME tails for an electrician of choice to connect into the excising setup. I suspect they have not done this yet and will do the actual conversion when an electrician is present.

Are you sure this is not a TT system?
Just reread all this and you are quite correct. OP where does the 25.0 earthing conductor go to I probably wrongly assumed it went to the head.
 

Reply to TNCS High ZE at origin in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
851

Similar threads

  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
981

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top