TNS DNO earth Braid | on ElectriciansForums

Discuss TNS DNO earth Braid in the Electrical Course Trainees Only area at ElectriciansForums.net

N

newtothis

I'd like to test, my house.
Pictured, is the DNO main earth in my house.

If I find the braiding is detriorated in anyway,
1. Can I replace with a 16mm earthing conductor ?
2. Or do I have to call the DNO ?
3. Should I just leave as is ?
4. What test could I do to prove it fit for purpose, or is it a case of looking up a table in the regs?

[ElectriciansForums.net] TNS DNO earth Braid
 
I'd be inclined to disconnect the outgoing earths rather than the braid since there's only a couple if them.
Or else reterminate the braid with a ferrule where it goes into the earth block.

With the exception of a wiped joint that's possibly the best connection you'll get on a lead cable, those clamps are tensioned with a special tool and the braid will likely offer a better ccc than a 16mm earth
 
as dave says. diss. your outgoing earths/bondings , and get your Ze. from the block and the incomer L in your CU.

i'll guess at a Ze of < 0.3 Ω
 
Last edited:
as dave says. diss. your outgoing earths/bondings , and get your Ze. from the block and the incomer L in your CU.
i'll guess at a Ze of < 0.3 Ω
Could I Diss. the outgoing earths, croc clip on to the braid just south of the met.
Then L+N top of the main switch. ?
Excuse me for being dim, :smile5: why do you say L and not L+N ?
 
because your Ze is measured from L -E. pscc from L-N and pefc L-E. ( for these last 2, your earths/bonding needs reconnecting)
 
Could I Diss. the outgoing earths, croc clip on to the braid just south of the met.
Then L+N top of the main switch. ?
Excuse me for being dim, :smile5: why do you say L and not L+N ?

I normally clip onto the braid as it gets a good bite on it.

Only L because you don't need N for a high current loop test. You only need an N for anti trip/low current tests.
You should only ever use the low current test option when it is impossible to use the proper high current test.
 
( for these last 2, your earths/bonding needs reconnecting)
LOL Yes indeed ! I've been frog-marched (rightfully so) out of a practical assessment for almost energising a circuit, with the DNO earthing dissed. Costly and inconvenent lesson learned. :)
 
I normally clip onto the braid as it gets a good bite on it.

Only L because you don't need N for a high current loop test. You only need an N for anti trip/low current tests.
You should only ever use the low current test option when it is impossible to use the proper high current test.

Yes thanks I understand, I will use the 2 lead option. If my rcd trips should I use the 3 lead test ?
 
Yes thanks I understand, I will use the 2 lead option. If my rcd trips should I use the 3 lead test ?

You should be testing from the incoming L of your (open) main switch to the supply earth. So the test current will be entirely upstream of any RCDs and not cause them to trip.

The anti trip/low current test is necessary on RCD protected circuits because the normal test passes a current between L and E which is greater than the 30mA tripping current of an RCD
 
Sorry I have my wires crossed, :skull:
I'm thinking about the PFC PSSC after the ZE
Due to what Telectrix said.

It's ok, you're learning so don't worry, just keep asking the questions and we'll do our best to help you.

You would still carry out those tests on the incoming side of the main switch so the test current will still be upstream of any RCDs
 

Reply to TNS DNO earth Braid in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top