The table in the top right shows that a 63 A will operate at 0.1 s at 820 A, so you can say at 900A it would be faster but if you take 0.1 s this will give a higher csa in the adiabatic if you then calculate for the earthing conductor and get a csa that is less than what you have at present then you are OK.
e.g. result is 2 mm² you have 6 mm² no problem.
Leesparkykent - that wouldn't be the relevant graph from the BRB by any chance LOL ?
Yeah it is
On a side note have I got a case for asking the DNO to upgrade the cut out ?
I been taught about asking for Ze by enquiry and stuff.
The reality with my DNO UKPN is they're not interested in anything that isn't an earner for them.
Thanks for the image.
The coin has dropped - I'm feeling very happy !
Before this I couldn't even read the graphs :rolleyes4:
And I gave the adiabatic a major body swerve.
I fairly confident I can consolidate what I've learned from this post and take it further.
Reply to TNS DNO earth Braid in the Electrical Course Trainees Only area at ElectriciansForums.net
Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!